Hello mates, how are all you?
Sirs, I'm having an issue by "Low Discharge Superheat" on a AWS INV 360.2 XE ST. My doubt is: How the Microtech III reconyze the "Discharge Temperature" to calculate the DSH? I couldn't find the Discharge Temperature Sensor on it. Someone can help?
-
24-02-2017, 07:08 PM #2
Re: McQuay Chiller Pathfinder
Discharge superheat = saturated discharge temp - discharge temp
-
25-02-2017, 10:21 AM #3
Re: McQuay Chiller Pathfinder
If it is Microtech-III the discharge sensor is DT-1 on wiring diagram. Check input X1 on board C.C.1