    Daikin VRV lV fire panel stop



    Hi, I have a Daikin VRV lV installed in a very small hotel. Recently the owners asked if there is a way to shut down the system if there is fire alarm. I know this can be done with the iTouch controller but this is quite expensive and would be a total waste as they just need that function. Is there any interface that can be connected to a volt free contact on the fire panel that will make the system shut down?

    Thanks in advance.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin VRV lV fire panel stop

    In short...yes there is.

    I would contact your local Daikin service centre who can recommend the right solution to your particular installation.

    KRP2A comes to mind

  3. #3
    Join Date
    Jun 2009
    Location
    Malta
    Age
    47
    Posts
    21
    Rep Power
    0

    Re: Daikin VRV lV fire panel stop

    Done that already but was told that the cheapeast option is the iTouch. So I was looking for another opinion. Thanks for your help Frank.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV lV fire panel stop

    buy the additional indoor terminal block with the t1 t2 contacts - open circuit stops indoor but u need to daisy chain it on all indoors- and change setting mode 13 to auto restart- or stick a contactor on the indoor ring main- not ideal but will keep fireman sam happy.

  5. #5
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin VRV lV fire panel stop

    ...or stick a contactor on the indoor ring main- not ideal but will keep fireman sam happy.

    This.

  6. #6
    Join Date
    Jun 2009
    Location
    Malta
    Age
    47
    Posts
    21
    Rep Power
    0

    Re: Daikin VRV lV fire panel stop

    Yep, sometimes I just forget the 'keep it simple, stupid' solutions.

    Many thanks to all.