Quote Originally Posted by Zoran_Popovski View Post
Hallo Mark
I have got the answers you are interested in:
- discharge temperature displayed on LED at first run is 19.7 degres,after 15 min.temp.rise to 64.5 degres
- pressure displayed on LED was17 bars,on the gauges was16.5 bars
Okay, what mode was the system in when you were measuring the discharge temperature? Going off that reading, I assume cooling mode?

Also what was the discharge pressure when the discharge temperature was at 64.5 degrees