Results 1 to 3 of 3
  1. #1
    Join Date
    Sep 2009
    Location
    Cyprus
    Age
    72
    Posts
    55
    Rep Power
    11
    SF-101S controller
    I could not obtain the parameter list for Husky under counter stainless steel fridge with the controller details given below.
    www.sfyb.com
    Model: SF-101S
    Scrolling through the parameter listed the parameters as below, some of them are not listed on the instruction manual of SF-101S
    Parameter list: E1,E2,E3,E4,E5,F1,F2,F4,H1,H2,H5,H6,CF,CPA
    Could anyone help?
  2. #2
    Join Date
    Sep 2009
    Location
    Cyprus
    Age
    72
    Posts
    55
    Rep Power
    11
    Re: SF-101S controller
    I have managed to resolve most of the issue. The parameters I have not manage to resolve are listed below.
    F4
    H1
    H2
    H5
    H6
  3. #3
    Join Date
    Sep 2009
    Location
    Cyprus
    Age
    72
    Posts
    55
    Rep Power
    11
    Going through all the parameters of the above mentioned controller.
    I have managed to identify all the parameters with the exception of H6 which has a factory default setting 00
    I have spent hours and visited instruction manuals of 184 models of the controllers supplied from the manufacturer.
    Non of them match the parameter configuration of the one I have got.
    On some models H parameters are for fan control and on some models are for humidity control.
    On the model I have got I have identified that, H parameters are high and low temperature alarm settings.