    Daikin U4 fault



    Hello guys
    Looking at a daikin fxts80gmvba. First fault was F3 so i changed discharge sensor outdoor sensor.
    Tried to run next fault was U4 fault.
    Any ideas im thinking the board?
    Thanks LJ



  2. #2
    Join Date
    Aug 2014
    Location
    Australia
    Age
    36
    Posts
    68
    Rep Power
    10

    Re: Daikin U4 fault

    Try unpluggging the outdoor fan motor. Then start unit up again. If comp starts to run then faults out with fan fault it's the fan. Also could be outdoor pcb like you suggested. Or Both, one could have taken out the other.

    Cheers, Keza

  3. #3
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: Daikin U4 fault

    It is sometimes confusing error.it might be the comp or the pcb or the outlet fan....who pays for all these parts?

  4. #4
    Join Date
    Jan 2012
    Location
    Uk
    Posts
    15
    Rep Power
    0

    Re: Daikin U4 fault

    Basics first you do still have power to the outdoor unit
    Check comms cables are connected