    delta t issue chilled water system



    need expert advise as i am facing issues with delta T attained in one of the site to which FM services are given

    District cooling supplies chilled water with 6 degree differential(supply 4.5 and return:11 degree Celsius)

    In my load side we are able to get approx 4 degree delta T only

    Supply been on a average of 7.5 and return 11 degree

    When referred O&M manual design which was noticed was to attain 23-24 degree celcuis supply air through AHU and FCU

    Client instructs to attain 20 to 21 degree celcuis on supply air

    could this possibly results in getting low delta T or is it due to some other factors



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: delta t issue chilled water system

    5-6 degrees delta T is fine, check for clean water filters and flow.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: delta t issue chilled water system

    Remind client that the system was designed for 23-24 and not 20-21.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: delta t issue chilled water system

    Delta t is directly related to water flow rate

  5. #5
    Join Date
    May 2010
    Location
    united arab emirates
    Age
    37
    Posts
    3
    Rep Power
    0

    Re: delta t issue chilled water system

    Thanks a lot for response given

    whether trying to achieve low supply air temperature(like 20 and 21) limits impact delta t or does it results in starving of chilled water at the index lines

  6. #6
    Join Date
    May 2010
    Location
    united arab emirates
    Age
    37
    Posts
    3
    Rep Power
    0

    Re: delta t issue chilled water system

    Strainers on our secondary side got cleaned recently .

    Constrain is that district cooling team supply the delta t as per the contract in the range 5-6 degree differential

    When it comes to our side conditions are not met(like able to attain 3 degree celcuis max. delta T).Also supply temperature to our building get served @ 7.5degree celcuis with district cooling side been 4.5 degree

    could you please help me in explaining why we come across such difference

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: delta t issue chilled water system

    Check and reset if necessary the chilled water flow rates through chillers, higher flow rates will reduce delta T, due to high tube flow rates and water dwell / retention time, lack of heat exchange.
    You have OEM manuals which should have commissioning settings per chiller set.