    May 2010
    united arab emirates
    32
    3
    delta t issue chilled water system
    need expert advise as i am facing issues with delta T attained in one of the site to which FM services are given
    District cooling supplies chilled water with 6 degree differential(supply 4.5 and return:11 degree Celsius)
    In my load side we are able to get approx 4 degree delta T only
    Supply been on a average of 7.5 and return 11 degree
    When referred O&M manual design which was noticed was to attain 23-24 degree celcuis supply air through AHU and FCU
    Client instructs to attain 20 to 21 degree celcuis on supply air
    could this possibly results in getting low delta T or is it due to some other factors
    Sep 2003
    ISRAEL
    66
    4,151
    38
    Re: delta t issue chilled water system
    5-6 degrees delta T is fine, check for clean water filters and flow.
    70
    10,602
    52
    Remind client that the system was designed for 23-24 and not 20-21.
    Oct 2001
    Nottingham UK
    5,123
    42
    Delta t is directly related to water flow rate
    I'm back on the Pale
    May 2010
    32
    3
    Thanks a lot for response given
    whether trying to achieve low supply air temperature(like 20 and 21) limits impact delta t or does it results in starving of chilled water at the index lines
    May 2010
    32
    3
    Strainers on our secondary side got cleaned recently .
    Constrain is that district cooling team supply the delta t as per the contract in the range 5-6 degree differential
    When it comes to our side conditions are not met(like able to attain 3 degree celcuis max. delta T).Also supply temperature to our building get served @ 7.5degree celcuis with district cooling side been 4.5 degree
    could you please help me in explaining why we come across such difference
    Auckland
    68
    3,362
    32
    Check and reset if necessary the chilled water flow rates through chillers, higher flow rates will reduce delta T, due to high tube flow rates and water dwell / retention time, lack of heat exchange.
    You have OEM manuals which should have commissioning settings per chiller set.