    Doule Jacketed tanks



    Hello
    I need a formula to calculate the Ton refrigerant to cool down some liquid from 22 c to 10 c in a double jacketed tank. The cooling media is water. I need to calculate the chiller capacity needed for this process.
    Thanks



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Doule Jacketed tanks

    Welcome to the forum Omar.

    To be able to calculate' please add a few parameters:
    - What is the mass? kg, ton?
    - Area of heat exchanging? sq/m.
    - insulation? Thickness and material.
    - No. of cooling circuits?

    The more details you supply [pictures are always helpful] the easiest it will be to help you.

  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Doule Jacketed tanks

    HI
    There is a lot of quition
    How much you need cool
    With whicth temp you want to rich to that
    What is you pump flow rates
    What is you tansfar heat area
    What is the insulation out of tanks
    What is the room temp.

    Q=MC(T2-T1)