Results 1 to 5 of 5
  1. #1
    Join Date
    Jan 2015
    Location
    England
    Posts
    15
    Rep Power
    0
    Discharge Superheat
    Hi Guys
    Your thoughts on this . .
    Liquid to liquid chiller on R410a with a Scroll comp
    Discharge pressure = 13bar
    Discharge Temp = 40c
    Discharge SH = 21.3C ??
  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    47
    Posts
    1,304
    Rep Power
    34
    Re: Discharge Superheat
    that would be correct calculation, only thing is that your discharge pressure is a bit low, what suction pressure have you and suction superheat?
    Mostly found in the southern part of this green and pleasant land.
  3. #3
    Join Date
    Jan 2015
    Location
    England
    Posts
    15
    Rep Power
    0
    Hi al
    Suction pressure is at 8 bar, temp is at 9.5c. SH = 5.8??
  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    47
    Posts
    1,304
    Rep Power
    34
    yep, 8b is 3.90c.
  5. #5
    Join Date
    Jan 2015
    Location
    England
    Posts
    15
    Rep Power
    0
    Many thanks al