    Discharge Superheat



    Hi Guys

    Your thoughts on this . .

    Liquid to liquid chiller on R410a with a Scroll comp

    Discharge pressure = 13bar
    Discharge Temp = 40c

    Discharge SH = 21.3C ??



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Discharge Superheat

    that would be correct calculation, only thing is that your discharge pressure is a bit low, what suction pressure have you and suction superheat?
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Jan 2015
    Location
    England
    Posts
    15
    Rep Power
    0

    Re: Discharge Superheat

    Hi al

    Suction pressure is at 8 bar, temp is at 9.5c. SH = 5.8??

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Discharge Superheat

    yep, 8b is 3.90c.
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Jan 2015
    Location
    England
    Posts
    15
    Rep Power
    0

    Re: Discharge Superheat

    Many thanks al