Thread: Discharge Superheat
-
11-01-2017, 04:07 PM #1
Discharge Superheat
Hi Guys
Your thoughts on this . .
Liquid to liquid chiller on R410a with a Scroll comp
Discharge pressure = 13bar
Discharge Temp = 40c
Discharge SH = 21.3C ??
-
12-01-2017, 01:01 AM #2
Re: Discharge Superheat
that would be correct calculation, only thing is that your discharge pressure is a bit low, what suction pressure have you and suction superheat?
Mostly found in the southern part of this green and pleasant land.
-
12-01-2017, 03:27 PM #3
Re: Discharge Superheat
Hi al
Suction pressure is at 8 bar, temp is at 9.5c. SH = 5.8??
-
16-01-2017, 12:27 AM #4
Re: Discharge Superheat
yep, 8b is 3.90c.
Mostly found in the southern part of this green and pleasant land.
-
22-01-2017, 09:05 PM #5
Re: Discharge Superheat
Many thanks al