    Unisab 2 possible slide position transmitter unisab ground fault ??



    Hello,

    I believe that I may have an issue with the unisab 2 board. At first I have suspected the slide position rotary transmitter to be at fault but after a number of setups and later, calibration of the transmitter. Along with putting in a new wire I accidently stumbled across a possible fault.
    I kept getting a reading 0.027A between the signal and ground, this would not adjust on the Span switch. Whilst testing on the bench I got the same reading when the ground connection was detatched.
    When I have the transmitter wired into the unisab I get the same reading.
    Do you know if there is a ground connection anywhere on the unisab board suitable other than those on the same terminal block as the transmitter. I want to test the resistance between the terminal or connection pin 30 (transmitter ground connection)and another ground for the vdc supply. Unfortunately I cant find one and wondered if anyonecan shed any light
    Any info would be very helpfull thank you.

    Kind regards ,Allan



  2. #2
    Join Date
    Apr 2016
    Location
    United Kingdom
    Age
    44
    Posts
    5
    Rep Power
    0

    Re: Unisab 2 possible slide position transmitter unisab ground fault ??

    Thanks anyway guys, after further checks I have ruled out the sensor. The unisab board is reacting strangely to the current coming from the sensor and the pcb is going to have to come out and be repaired or replaced. That should be fun.

  3. #3
    Join Date
    Oct 2016
    Location
    Serbia
    Age
    51
    Posts
    110
    Rep Power
    8

    Re: Unisab 2 possible slide position transmitter unisab ground fault ??

    Hi allanjones,first of all Happy New Year and Merry Christmas,I "fight" with Sabroe for last 18 years.From my experience you have problem with position transmiter(the old one),magnetic coupling,or main relay board(factory sad life of the board is app.10 years).