12-05-2006, 02:15 PM #1
temperatures of the suction and discharge lines
HI There All
Can anybody please confirm that the suction tempreature on a R22 and R407c system should be between 0 and 5 deg c.
The discharge around 60 and 70 deg c.
If i am not mistaken this is a more acurate way of working out if the system is low on refrigerant bearing in mind that there is no hot gas bypass and the expansion valve is working correctly and giving you a superheat of +-5 deg c
Victor
12-05-2006, 11:37 PM #2
Re: temperatures of the suction and discharge lines
Sounds reasonable, after all you are not trying to freeze anything only cool the air.
15-05-2006, 09:47 PM #3
I might be wrong but my general rule of thumb is you should not have any lower than 7 degrees C going back to your compressor. So if R22 with a suction pressure of about 60 psi(g) and a suction pipe temp of 7 degrees C would be 7 degrees superheat. Ideal
16-05-2006, 05:00 AM #4
Hi VIXS,
Welcome to the RE forum.
I also think it is important to understand the relevance of the discharge temperature and discharge superheat as a function of the suction superheat.
Please also bear in mind the different refrigerants will have a different specific heat ratio for each refrigerant.
A refrigerant with a high specific heat ratio will produce a higher discharge temperature than a refrigerant with a lower specific heat ratio at the same operating conditions.
Suction superheat is only one measure of a systems' performance, which might not be dependent on refrigerant charge alone.
17-05-2006, 07:18 AM #5
Originally Posted by US Iceman
CARE refigerants by BOC
By dogma in forum RefrigerantsReplies: 8Last Post: 23-03-2010, 12:39 PM -
Interesting Problem
By NH3LVR in forum Industrial CompressorsReplies: 13Last Post: 12-08-2006, 10:27 PM -
Bearing trouble - rotary compressor
By rosetennis in forum Industrial CompressorsReplies: 6Last Post: 18-05-2006, 01:26 AM -
Exploded discharge line
By Peter_1 in forum IndustrialReplies: 1Last Post: 05-05-2004, 09:47 PM