    Question temperatures of the suction and discharge lines



    HI There All

    Can anybody please confirm that the suction tempreature on a R22 and R407c system should be between 0 and 5 deg c.
    The discharge around 60 and 70 deg c.
    If i am not mistaken this is a more acurate way of working out if the system is low on refrigerant bearing in mind that there is no hot gas bypass and the expansion valve is working correctly and giving you a superheat of +-5 deg c

    Victor



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: temperatures of the suction and discharge lines

    Sounds reasonable, after all you are not trying to freeze anything only cool the air.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Red face Re: temperatures of the suction and discharge lines

    I might be wrong but my general rule of thumb is you should not have any lower than 7 degrees C going back to your compressor. So if R22 with a suction pressure of about 60 psi(g) and a suction pipe temp of 7 degrees C would be 7 degrees superheat. Ideal

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: temperatures of the suction and discharge lines

    Hi VIXS,

    Welcome to the RE forum.

    I also think it is important to understand the relevance of the discharge temperature and discharge superheat as a function of the suction superheat.

    Please also bear in mind the different refrigerants will have a different specific heat ratio for each refrigerant.

    A refrigerant with a high specific heat ratio will produce a higher discharge temperature than a refrigerant with a lower specific heat ratio at the same operating conditions.

    Suction superheat is only one measure of a systems' performance, which might not be dependent on refrigerant charge alone.

  5. #5
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Talking Re: temperatures of the suction and discharge lines

    Quote Originally Posted by US Iceman

    Suction superheat is only one measure of a systems' performance, which might not be dependent on refrigerant charge alone.
    I agree US Iceman, by measuring the suction superheat you are only confirming that the evaporator is performing correctly.

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  3. Interesting Problem
    By NH3LVR in forum Industrial Compressors
    Replies: 13
    Last Post: 12-08-2006, 10:27 PM
  4. Bearing trouble - rotary compressor
    By rosetennis in forum Industrial Compressors
    Replies: 6
    Last Post: 18-05-2006, 01:26 AM
  5. Exploded discharge line
    By Peter_1 in forum Industrial
    Replies: 1
    Last Post: 05-05-2004, 09:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •