Results 1 to 12 of 12
    Aug 2016
    India
    8
    Ice formation at low side of compressor
    hi friends how are you all?
    As i have joined new compny here R-404a, system of Bitzer comp rack system are installed for blast freezers. there is ice formation in all comps at suction side of each comps, the contractor is saying this is due to Low condensation , as here the climet is very cold so condensation is not proper. what are the possibilities? plzz suggest me i am new to ***** refrigeration system.
    ireland
    54
    275
    Re: Ice formation at low side of compressor
    Ice forming on the suction flanges is quite normal for low temp applications , If you were evaporating at -28c and you had 20k super heat at compressor your suction gas would still be entering compressor at -8c and ice would form . Check your super heat to reassure yourself you have no liquid and all is good . Personally id be more worried if i had no ice forming at low temp applications unless the run was very long.
    Aug 2016
    India
    8
    Ice is farming on compressor at suction side, and contractor is saying need to calibrate fan and pump differential switch, and also to replace the filters and suction line strainer.
    Feb 2007
    2,473
    First of all, the ice is formed because of the cold temperature of the suction gas that is "coming back" to the compressor.
    Without having any knowledge about your installation, the ice forming is most likely normal and nothing to worry about. The important thing to look for is that the refrigerant returning to the compressor is superheated and that the oil isn't washed out of the compressor by liquid refrigerant.
    Cold climate would aid condensation, not hinder it. Over-condensation, whereas too much refrigerant is held in the condenser, could happen during cold ambient temperatures but this, on it's own, would not cause suction side ice build up and is more likely to present itself as poor performance or a shortage of refrigerant.
    Over-condensation can be prevented by proper system design, most commonly by including fan speed control for condenser fans.
    Jan 2007
    India
    65
    As you mentioned blast freezer I guess the temperature requirement in the range of -20 to -40 C . If so you would see ice formation in the low side and it is normal. Replacing filter drier or strainer is not necessary unless the sight glass turns wet. Please measure the suction pressure and compressor shell temperature that tell us either compressor is safe or not
    Sep 2009
    Iran
    66
    672
    1
    Our friends told every thing
    Also be careful about ice goes to conection electric box on the compressor and might you need to put heater inside and out side of that and it should be good sealed from out side weather
    This is very very important
    ireland
    54
    275
    Good point mbc ,years ago when i did ice plants we used to grease over the compressor terminals to stop any water forming around them , Even though the ice rarely forms past the compressor flange you could get a nice sweat running a bit up the compressor as the line sets used to be short on them.
    Aug 2016
    India
    8
    thanku guyz for all your replies.....and sharing this kind imp knoweldge..thanks for all
    Have you checked the compressor suction super heat is at or above compressor manufacturers minimum level.
    The purist desk jockey engineers say, the enthalpy of saturated suction vapor at correct suction super will not form hard crusted ice at suction valve.
    Magoo
    Jan 2008
    Albania
    71
    Try to close little expansion valve
    Feb 2001
    Doncaster, England
    199
    Don't touch the expansion valve until you have checked the suction superheat.
    Tony
    Sep 2009
    Iran
    66
    672
    1
    Good pint tony told
    To touch of expansion is last one
    Check all option might can happen
    Fans working
    Defrost
    To much opening of door
    And...
    And last one should be expansion