    Designing Accumaltor



    Hi,

    I need some advise and basic fundamentals on designing accumulator for R717 flooded Evaporator.

    Previously I designed accumulator had no coils and I am seriously thinking to modify and make some new.

    I have evaporator of 77 KW rated, so based on my idea 5 feet (1.5 Meter) x 2 feet (0.6 meters) should be sufficient.

    The problem is coil. I made some research and I am not sure if "hot line" coil could be inside of accumulator or outside.
    See below link:
    https://www.google.ch/patents/US6463757

    There are some more accumulators I saw which is U type but that one I saw mostly for freeon.

    I would appreciate if someone can help me with design and share with me their existingacc.png designs.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Designing Accumaltor

    what is the evaporator SST., are you designing for?. High pressure liquid feed to coil?. Pumped liquid feed, gravity feed ?.
    Horizontal accumulators have a larger surface area reducing surge levels, plus adding a serpentine sub cooling circuit in bottom of vessel is ok. Add oil trapping and drain as well. Add high level alarms.

  3. #3
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Designing Accumaltor

    Hi
    Evoperator temperature is +3.0 C
    High pressure I am plannint to feed to could
    No Pump would be installed
    Gravity feed yes.
    plus adding a serpentine sub cooling circuit in bottom of vessel is ok.
    I did not understand what is serpentine sub cooling circuit.
    Should it be inside accumulator?
    or just wrap around outside accumulator?

  4. #4
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Designing Accumaltor

    Hi
    Would appreciate if some one can shed expert opinion on above.

  5. #5
    Join Date
    Mar 2010
    Location
    Lisbon
    Posts
    55
    Rep Power
    17

    Re: Designing Accumaltor

    Hi skhan855,
    I canīt understand why you pretend to use a suction accumulator with heat exchanger to feed a NH3 evaporator. I can't see any usefull purpose. Those kind of apparatus are used for compressor suction protection with halogenated fluids, not NH3.
    For NH3 gravity feed evaporators I only know basic separators, they can be horizontal or vertical, but without any heat exchanger.

  6. #6
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Designing Accumaltor

    The reason for this is that icing occurs in suction accumulator.
    The safety float switch would trip occasionally when it reach safety level.

    Wouldn't heat exchanger would improve performance of system?

  7. #7
    Join Date
    Aug 2016
    Location
    India
    Age
    65
    Posts
    1
    Rep Power
    0

    Re: Designing Accumaltor

    Dear S Khan
    you are trying to work with Accumulator with Flooded system, Please find enclosed a P&I diagram of the same, it is orignally a diagram for hot gas defrost system, and not to confuse you I have cut the hot gas line. Difference in this diagram and what you are doing is that in diagram an ACU has been shown and you are using a Coil which will be filled with R717 and a Thermosiphon is created. coil shall be kept in the cylindricalNew Picture (2).jpg drum, which would have liquid (Water/brine/gyclol) which you wish to cool

  8. #8
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Designing Accumaltor

    Hi
    I could not study diagram as file size is too small to read, I see you are new to forums and there is a way attaching a image file. you need to click on third last icon where it says insert a image (on mouse hover) and attach file.

  9. #9
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Designing Accumaltor

    Quote Originally Posted by skhan855 View Post
    Hi
    I could not study diagram as file size is too small to read, I see you are new to forums and there is a way attaching a image file. you need to click on third last icon where it says insert a image (on mouse hover) and attach file.
    skan855,
    I am confused, which type of system are you designing

    1/ Liquid recirculation with liquid pump
    2/ AKVA type expansion valve with accumulator(slop pot, suction trap) in plant room with boil of coil in it (serpentine coil, high pressure liquid line to evaporators running inside suction accumulator in a separate coil
    to boil off any refrigerant that returns from evaporator for any reason to protect compressor).
    3/ gravity feed surge drum mounted over the top of evaporator/s using thermosyphon principle.

    1/ most expensive liquid recirculation
    3/ less expensive used with 1-6 separate evaporators approximately
    2/ cheapest

    You mention long lead time of 6 weeks for AKVA valves, what is lead time on the rest of the equipment?

  10. #10
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Designing Accumaltor

    Hi
    Situation is like this.

    System is gravity mode

    I am planning to install hand expansion valve without concept of Super hear / AKVA. However
    Solenoid valve would be installed for each evaporator.

    Excess liquid coming from Evaporator would be stored in its own Accumulator; this means each evaporator will have its own accumulator.

    Each accumulator will have its own AKS 38 or similar float switch which will signal respective evaporator solenoid to shut off despite target temperature achieved. Further solenoid will be switched off through a temperature controller once temperature achieved.

    Now to avoid frequent tripping signals from AKS38 or similar, I want to install serpentine coil so that excess liquid evaporates.

    I don’t know how to make accumulator with serpentine coil, but I can make it because I make condenser and evaporators and accumulators without serpentine coil.

    I am attaching a diagram based on my understanding; please check if I am on right track. Please pay attention to 1 and 2 on receiver connecting serpentine coil is it OK?

    AKVA in Pakistan costing me USD 740 which is too high compare to international price of USD 550 + lead time too high. I think hand expansion is ok
    Attached Images Attached Images
    Last edited by skhan855; 21-08-2016 at 10:23 AM.

  11. #11
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Designing Accumaltor

    Skhan855,
    I don't think this will work at all.
    Firstly liquid line should leave liquid receiver, go through coil in accumulator to potentially boil off any liquid that returns from evaporator., then to expansion device on evaporators.
    Also you need an expansion device on each evaporator to control superheat.
    If you return to much liquid to accumulator, your in trouble as how to transfer it back to liquid receiver!
    In this case accumulator helps boil off excess liquid ammonia & protects compressor.
    There are ammonia TX valves like Danfoss,Sporlan, Parker to name a few, which are cheaper than AKVA, but control in not as good as electronic valve.
    Last edited by RANGER1; 21-08-2016 at 10:38 PM.

  12. #12
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Designing Accumaltor

    Hi,
    I have run system for some months with manual expansion valve and without AKS 38, everything manually and all worked fine.

    The problem I am facing with existing scenario is that too much liquid coming to Accumulator. For that there would be two options.

    1) install AKVA or similar expansion along with AKS 38 on accumulator, but I spoke with some installers and technicians, they advise me that since system is in flooded mode therefore I don't know TXV or AKVA.
    Hand valve is more than enough. This practice is normal in India and Pakistan. I am confused between your method and what I got suggestions from Indian and Pakistani technicians.

    2) Install a Solenoid and AKS 38 that turns off Solenoid as soon as accumulator reached dead level. This is Indian method.

    but in any case I need to install serpentine coil and I am not clear with connections of it. So far I understand from you that:
    Liquid Line -> serpentine coil -> Expanssion valve -> Evoperator

    Please find correct attached diagram marked as 1 and 2

    I myself is good in electronics and do basic programming, and could control AKVA + pressure transducer.
    design2.jpg

  13. #13
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Designing Accumaltor

    hansen have pulse ammonia liquid expansion valve suitable for each evaporator, to eliminate excessive carry over, search Hantech PXVW 60.
    and make surge vessel horizontal with sub cooling coil in the bottom

  14. #14
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Designing Accumaltor

    Hi, I got solution to install actuator on expanssion valve, which I can control through PLC, this will open close hand valve to 90 Degree, that is half turn of 1 round.

    Any particular reason to make horizontal accumulator?

  15. #15
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Designing Accumaltor

    I have never seen horizontal one, only vertical.
    Vertical takes up less space & easier to run liquid line boil off coil inside.
    Horizontal one with coil in bottom a lot more work to fit as much pipe as possible.

  16. #16
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Designing Accumaltor

    Hi,
    Are connection ok? 1 and 2design2.jpg

  17. #17
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Designing Accumaltor

    Looks OK to me, evaporator regulating valves are a concern, as never seen them used in that way.
    Do evaporators have a distributor set up for TX valve?

  18. #18
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Designing Accumaltor

    Evaporator regulator valve, you mean Expansion valve?

  19. #19
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Designing Accumaltor

    Quote Originally Posted by skhan855 View Post
    Evaporator regulator valve, you mean Expansion valve?
    Yes sounds unreliable to me, needs to control superheat on suction of evaporator. Hand expansion valve closed to much poor performance, if open to far flood back of liquid ammonia to accumulator.
    Last edited by RANGER1; 24-08-2016 at 08:31 PM.

  20. #20
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Designing Accumaltor

    Hi,
    I am working on actuator, to control expansion valve. we will have results in dry test how much it can open / close.

  21. #21
    Join Date
    Feb 2017
    Location
    India
    Posts
    1
    Rep Power
    0

    Re: Designing Accumaltor

    Hi, what is the alternative for the accumulator to store liquid refrigerant in the fridge?