    Ice formation at low side of compressor



    hi friends how are you all?
    As i have joined new compny here R-404a, system of Bitzer comp rack system are installed for blast freezers. there is ice formation in all comps at suction side of each comps, the contractor is saying this is due to Low condensation , as here the climet is very cold so condensation is not proper. what are the possibilities? plzz suggest me i am new to ***** refrigeration system.



  2. #2
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Ice formation at low side of compressor

    Ice forming on the suction flanges is quite normal for low temp applications , If you were evaporating at -28c and you had 20k super heat at compressor your suction gas would still be entering compressor at -8c and ice would form . Check your super heat to reassure yourself you have no liquid and all is good . Personally id be more worried if i had no ice forming at low temp applications unless the run was very long.

  3. #3
    Join Date
    Aug 2016
    Location
    India
    Age
    37
    Posts
    8
    Rep Power
    0

    Re: Ice formation at low side of compressor

    Ice is farming on compressor at suction side, and contractor is saying need to calibrate fan and pump differential switch, and also to replace the filters and suction line strainer.

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Ice formation at low side of compressor

    First of all, the ice is formed because of the cold temperature of the suction gas that is "coming back" to the compressor.
    Without having any knowledge about your installation, the ice forming is most likely normal and nothing to worry about. The important thing to look for is that the refrigerant returning to the compressor is superheated and that the oil isn't washed out of the compressor by liquid refrigerant.

    Cold climate would aid condensation, not hinder it. Over-condensation, whereas too much refrigerant is held in the condenser, could happen during cold ambient temperatures but this, on it's own, would not cause suction side ice build up and is more likely to present itself as poor performance or a shortage of refrigerant.
    Over-condensation can be prevented by proper system design, most commonly by including fan speed control for condenser fans.


  5. #5
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: Ice formation at low side of compressor

    As you mentioned blast freezer I guess the temperature requirement in the range of -20 to -40 C . If so you would see ice formation in the low side and it is normal. Replacing filter drier or strainer is not necessary unless the sight glass turns wet. Please measure the suction pressure and compressor shell temperature that tell us either compressor is safe or not

  6. #6
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Ice formation at low side of compressor

    Hi
    Our friends told every thing
    Also be careful about ice goes to conection electric box on the compressor and might you need to put heater inside and out side of that and it should be good sealed from out side weather
    This is very very important
    Last edited by mbc; 26-12-2016 at 05:55 PM.

  7. #7
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Ice formation at low side of compressor

    Good point mbc ,years ago when i did ice plants we used to grease over the compressor terminals to stop any water forming around them , Even though the ice rarely forms past the compressor flange you could get a nice sweat running a bit up the compressor as the line sets used to be short on them.

  8. #8
    Join Date
    Aug 2016
    Location
    India
    Age
    37
    Posts
    8
    Rep Power
    0

    Re: Ice formation at low side of compressor

    thanku guyz for all your replies.....and sharing this kind imp knoweldge..thanks for all

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Ice formation at low side of compressor

    Have you checked the compressor suction super heat is at or above compressor manufacturers minimum level.
    The purist desk jockey engineers say, the enthalpy of saturated suction vapor at correct suction super will not form hard crusted ice at suction valve.
    Magoo
    Last edited by Magoo; 30-12-2016 at 11:50 PM.

  10. #10
    Join Date
    Jan 2008
    Location
    Albania
    Age
    71
    Posts
    21
    Rep Power
    0

    Re: Ice formation at low side of compressor

    Try to close little expansion valve

  11. #11
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: Ice formation at low side of compressor

    Don't touch the expansion valve until you have checked the suction superheat.
    Tony

  12. #12
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Ice formation at low side of compressor

    Hi
    Good pint tony told
    To touch of expansion is last one
    Check all option might can happen
    Fans working
    Defrost
    To much opening of door
    And...
    And last one should be expansion