    Dec 2016
    Australia
    3
    Glycol s/steel lines is purging required?
    Hi all, we are installing a glycol system, I have 2 opinions, ones says we don't need to purge the s/steel glycol lines and the other is recommending that we do it to provent corrosion
    Glycol temp is 0c,
    S/steel lines, 304. 1.6mm
    The glycol is propylene,
    Any advise would be much appreciated!!
    10,505
    Re: Glycol s/steel lines is purging required?
    I don't know about purging but you will need air vents.
    Croatia
    2,127
    Hi, Micbon
    Welcome to RE forums...
    Quote Originally Posted by Micbon View Post
    Glycol temp is 0c,
    Probably you are thinking either to use or not shield gas during welding of your pipes ... argon or helium .... otherwise your job will be done at very low quality ... weld repairing is always more expensive then good welding procedure from beginning ... but you are the boss
    I am not a welding specialist ... the best is to check here http://smt.sandvik.com/en/products/w...ielding-gases/
    and some other places.
    Best regards, Josip
    Dec 2016
    Australia
    3
    Thanks guys! Yes thinking weather to purge pipes with argon during welding, don't want trouble down the track!
    Best regards
    Aug 2010
    110
    8
    It is generally accepted good engineering practice but if you are talking about large bore pipes 4" and above I would say its an irrelevance. Corrosion is also not relevant as most glycol mixes carry an inhibitor and you did say it was stainless. On smaller pipes I would go for purging if the cost was not too great as the weld can sometimes induce noise and turbulence in the flow pattern. Brian_UK did mention air vents and this is important I would install a Tee piece at the highest point in both supply and return with the Tee being the same dimension as the pipe.
    Dec 2016
    Australia
    3
    Thanks for the advise piewie!