    Question York YVAA - Low Suction Pressure Issue



    Hi,

    I have a York YVAA Chiller operating at my plant. From the past few weeks, the unit trips randomly on fault of "LOW SUCTION PRESSURE".

    The unit is running on a low load, and the Difference between the Entering and Leaving is 5 Degrees C (Setpoint/Leaving: 7 Degrees, Entering: 12 Degrees).

    I have checked all the valves/sensors and they are okay. Can someone tell me what else i need to check and what could be the cause of this?



  2. #2
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: York YVAA - Low Suction Pressure Issue

    Your chiller sounds like it is low on refrigerant as the TD is correct but it is not loading up and giving low suc alarm.

    If it is a newer model with aluminium micro channel condensing coils your leak will be in this area.