    Re: Propylene System

    Besides the above puzzle, I have the same thinking to the ammonia system.The present water in the R717 system maybe cause the same trouble,don't it?But in the R717 system there isn't filter-dryer.What happend?
    solubility of water with refrigerants?

  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Propylene System

    Quote Originally Posted by sagittarius
    The present water in the R717 system maybe cause the same trouble, don't it? But in the R717 system there isn't filter-dryer. What happened?
    Ammonia is hygroscopic. It will absorb water just like a drier will. The ammonia will continue to absorb water until it reaches a saturated point. As the ammonia continues to absorb water the pressure/temperature relationship is changed. You have to run lower and lower evaporating pressures to obtain the same temperature without the water being present.

    Driers are available for ammonia, but not normally used.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •