Results 1 to 2 of 2
    Apr 2006
    china
    7
    propylene refrigerant
    When we use propylene as regrigerant in screw refrigeration cycle,what kind of oil should we choose_whole dissolve or part dissolve with oil?and if we need dry filter?
    Aug 2005
    5,302
    Re: propylene refrigerant
    You need to check the dilution data for the specific oil and operating conditions (pressure & temperature).
    The compressor will have certain viscosity requirements to provide lubrication to rotating parts. The amount of dilution decreases the oil viscosity, so you may have to use a more viscous oil than normally thought.
    You also need to be careful with oil pour points for low temperature use.
    Synthetic oils tend to work much better as they are more stable. However, they can be very expensive.
  1. R600 Refrigerant.
    By tonydeith in forum Refrigerants
    Last Post: 21-04-2011, 08:52 AM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Last Post: 23-03-2010, 12:39 PM
  3. Replies: 2
    Last Post: 16-11-2005, 05:34 PM
  4. Liquid refrigerant and bubles in sightglass
    By aygul in forum Trouble Shooting
    Last Post: 30-08-2003, 09:07 PM
  5. Refrigerant Reclamation
    By herefishy in forum Commercial
    Last Post: 23-07-2003, 08:19 AM