    dirty condenser signal light



    I am looking to install a light to signal when the condenser is dirty so the user could perform maintanence. It would come on before the high pressure cutout trips. I see two possibilities. One being a fan cycle control that makes contact on rise of pressure just below the safety cutout and lites the signal that the unit needs cleaning. Or a temp control with probe strapped to the hot gas line doing the same thing.
    My question is which would be prefered and where would I sample the pressure or temperature to initiate the sequence. Thanks, Ken



  2. #2
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: dirty condenser signal light

    why not fit another h/p control or an encapusulated pressure switch with a fixed range
    mmm to beer or not to beer...........lets drink breakfast

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: dirty condenser signal light

    .....or a differential pressure switch over the condenser

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: dirty condenser signal light

    Why not get the user to enter into a maintenance agreement.

    That way they don't have to think about it because you will do the work for them and that is how the money goes around.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: dirty condenser signal light

    why not fit another h/p control or an encapusulated pressure switch with a fixed range
    This would defiately be the way to go but
    I have tried to find an encapsulated switch that makes on rise that has the right Make and Break psi. it seems they are only made as safteys and break on rise which would then require a relay further complicating things.
    Why not get the user to enter into a maintenance agreement
    .
    I work for the manufactuer that wants more sizzle on thier steak. Just started using a ranco fan cycler connected to the hot gas line. It works but the differential is wider than desired. I have been thinking or using the carel control that has a third temperature probe which could possibly used to turn on an indicator light

    Am I ok connected to the hot gas before the condenser or would the liquid line be beter? ..Ken
    Last edited by kengineering; 13-03-2010 at 04:27 PM.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: dirty condenser signal light

    I would go with cond dT.

  7. #7
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: dirty condenser signal light

    Gary, I had thought of that but just couldn't figure out how to get it done. Suggestions? Ken

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: dirty condenser signal light

    Quote Originally Posted by kengineering View Post
    Gary, I had thought of that but just couldn't figure out how to get it done. Suggestions? Ken
    Do I get a consulting fee?

    Monitor the temps of the air entering and leaving the condenser, subtract entering from leaving, trip the alarm when the difference (dT) exceeds pre-determined value.

    Of course, if the fan speed is controlled the alarm would only be enabled when the fan is running 100%.

  9. #9
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: dirty condenser signal light

    I'll look you up next time I go fishing in FL. for that consult fee. Although we're just tring to hold on to our jobs here in NJ. It could be a while.

    Just to clarify. I'm not actually cycling a fan with the Ranco. Set around 400 psi coil gets dirty, head goes up switch makes and lites an indicator. After cleaning the coil the lower head pressure is realised with the differntial set , lite goes out. It works fine and so far reliable but it's clunky.

    I couldn't come up with a simple delta-T system.

    My next attempt will be to get an accurate temp reading on the hot gas line. strap a temp probe with a programed temp and differential too turn the lite on and off. Then I can make a choice from a production standpoint.

    Just trying to think of all possibilities. Thanks , Ken
    Last edited by kengineering; 13-03-2010 at 05:48 PM.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: dirty condenser signal light

    Quote Originally Posted by kengineering View Post
    I
    I couldn't come up with a simple delta-T system.

    http://www.ojelectronics.com/Differe...mostat-65.aspx

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: dirty condenser signal light

    That looks like a winner to me, Nike.

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: dirty condenser signal light

    Or this ESF-35-1 airflow transducer with relay:
    http://www.ojelectronics.com/AIRFLOW...DUCERS-97.aspx

  13. #13
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: dirty condenser signal light

    their are electronic controllers with this function,sensing liquid line temp,in alarm state the display flashes with its fault code.

    oops i see you have already mentioned carel,definitly the easier way out me thinks
    Last edited by lowcool; 14-03-2010 at 12:41 AM.
    mmm to beer or not to beer...........lets drink breakfast

  14. #14
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    297
    Rep Power
    14

    Re: dirty condenser signal light

    ever thought about a three month timer ?

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: dirty condenser signal light

    ever thought about a three month timer
    Zelio!........

  16. #16
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    297
    Rep Power
    14

    Re: dirty condenser signal light

    why make it more complex than it has to be sorry if my timer idea offends just seemed simple if condenser blocks regularly put a timer in for optimal time less to go wrong

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  2. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  3. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  4. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Replies: 11
    Last Post: 02-03-2008, 07:10 PM
  5. How many forum posters does it take to change a light bulb....
    By taz24 in forum Chit Chat & Service Stories
    Replies: 7
    Last Post: 04-02-2008, 08:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •