    Dec 2016
    Israel
    3
    Help needed with bitzer screw, please
    Hi guys,
    I have a Climaveneta chiller runing with this bitzer screw
    CSH-8591-140CVY-40P.
    The compressor is loosing oil like crazy, any Ideas anyone?
    Tamir
    3,355
    Re: Help needed with bitzer screw, please
    Tamir,
    Tell us a bit more about system.
    Does it lose oil when running, or if cycled off?
    What type of oil separator/s does it have, any coalescer type, is oil return working?
    Is it getting floodbacks?
    Is it a new system, has it worked OK in the past?
    A few pictures etc
    Dec 2016
    Israel
    3
    HI Ranger,
    its a climaveneta Italian chiller.
    Yes its losing oil only when running, when the compressor shuts down the oil returns after a few minutes.
    It has an internal oil separator (you can see in the pictures).
    this compressor got a tiny overhaul , bearings and gasket replaced.
    the system worked fine before.
    Many Thanks
    Feb 2007
    2,473
    Most likely issues;
    - Lack of refrigerant
    - Poorly adjusted EEV/TEV
    - Oil line/flow issues
    Dec 2016
    Israel
    3
    Hi Viking
    I check all the above and they are fine.
    Its the weirdest thing, the compressor can run 10 minutes and lose the oil or it can happen after 7 hours...
    Its runing on r134a with solest170 oil..
    Any chance that an jamed oil filter can cause the issue?
    3,355
    Quote Originally Posted by Tamir View Post
    Hi Viking
    Tamir,
    What about to much refrigerant washing oil out!
    Check out expansion valve & bulb etc, superheat, liquid line solenoid, filter drier, water flow.
