    Help needed with bitzer screw, please



    Hi guys,

    I have a Climaveneta chiller runing with this bitzer screw
    CSH-8591-140CVY-40P.

    The compressor is loosing oil like crazy, any Ideas anyone?
    Thanks
    Tamir



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Help needed with bitzer screw, please

    Tamir,
    Tell us a bit more about system.
    Does it lose oil when running, or if cycled off?
    What type of oil separator/s does it have, any coalescer type, is oil return working?
    Is it getting floodbacks?
    Is it a new system, has it worked OK in the past?

    A few pictures etc

  3. #3
    Join Date
    Dec 2016
    Location
    Israel
    Posts
    3
    Rep Power
    0

    Re: Help needed with bitzer screw, please

    HI Ranger,

    its a climaveneta Italian chiller.
    Yes its losing oil only when running, when the compressor shuts down the oil returns after a few minutes.
    It has an internal oil separator (you can see in the pictures).
    this compressor got a tiny overhaul , bearings and gasket replaced.

    the system worked fine before.

    Many Thanks
    Tamir20161212_065407.jpg20161212_065423.jpg20161212_065427.jpg20161212_072101.jpg

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Help needed with bitzer screw, please

    Most likely issues;
    - Lack of refrigerant
    - Poorly adjusted EEV/TEV
    - Oil line/flow issues


  5. #5
    Join Date
    Dec 2016
    Location
    Israel
    Posts
    3
    Rep Power
    0

    Re: Help needed with bitzer screw, please

    Hi Viking

    I check all the above and they are fine.
    Its the weirdest thing, the compressor can run 10 minutes and lose the oil or it can happen after 7 hours...

    Its runing on r134a with solest170 oil..

    Any chance that an jamed oil filter can cause the issue?

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Help needed with bitzer screw, please

    Quote Originally Posted by Tamir View Post
    Hi Viking

    I check all the above and they are fine.
    Its the weirdest thing, the compressor can run 10 minutes and lose the oil or it can happen after 7 hours...

    Its runing on r134a with solest170 oil..

    Any chance that an jamed oil filter can cause the issue?


    Tamir,
    What about to much refrigerant washing oil out!
    Check out expansion valve & bulb etc, superheat, liquid line solenoid, filter drier, water flow.