    Daikin mono bloc 16kw for just radiators



    Can any one help we just need to heat the radiators up to 40 can we just put this on to the old existing system we do not need to do hot water do we need a tank with this ? Or can it go straight on to the return and flow the system is going on to a house in the algarve Portugal and is used for 8 weeks of the year



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    501
    Rep Power
    16

    Re: Daikin mono bloc 16kw for just radiators

    Provided that you have thoroughly flushed the system to remove any debris, you could use the mono block to provide heating input only.
    Probably best to install an inline filter such as the Fernox TF1 to provide extra filtration for the water circuit.
    If the unit is going to be turned off in the cold weather then it would be best to use a special heat pump antifreeze solution such as Fernox HP-5C to a suitable protection level..
    You would be able to achieve a maximum flow temperature of 55 degrees, if needed.
    Obviously the system would be much more efficient at the lower flow temperatures.
    There is no need to have a hot water tank as you can set the system up in a heating only mode.
    You can then control the unit by a remote thermostat across terminals 1 & 4 and preset the flow temperature or have it weather compensated.
    Mobile A/C at its best, see avatar.

  3. #3
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    47
    Posts
    168
    Rep Power
    10

    Re: Daikin mono bloc 16kw for just radiators

    Thank you for your help

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    67
    Posts
    3,362
    Rep Power
    31

    Re: Daikin mono bloc 16kw for just radiators

    If not already fitted, install automatic air bleeders at highest point of water circuit. Will stop all banging and clanging in the pipework.

  5. #5
    Join Date
    Feb 2008
    Location
    Portugal
    Age
    47
    Posts
    168
    Rep Power
    10

    Re: Daikin mono bloc 16kw for just radiators

    They have been fitted thank you Magoo

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,061
    Rep Power
    42

    Re: Daikin mono bloc 16kw for just radiators

    If your existing system is 'Vented' type (expansion tank in the loft) and you change to 'Unvented', (pressurised) you may end up with a few leaks