    Samsung air to water heat pump



    I have a problem with a Samgsung RC160 MHX EA air to water heat pump. The fault code was high pressure problem. I fitted my gauges and noticed the low pressure going down to zero. I am assuming the expansion valve is where the problem is and it trips on high pressure as the refrigerant liquid is filling the plate heat exchanger. The number on the expansion valve is SXK 06 and its 12 v dc. My question is how do I find out if the expansion valve is at fault or if its not getting a signal to open? Any help would be greatly appreciated



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Samsung air to water heat pump

    Have you checked the water flow rate?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2008
    Location
    Scotland
    Age
    60
    Posts
    29
    Rep Power
    0

    Re: Samsung air to water heat pump

    when I saw it was a high pressure fault water flow was my first thoughts. Is there a sensor what would keep expansion valve from opening if not enough water flow? The compressor discharge pipe did not rise above 27c

  4. #4
    Join Date
    Nov 2008
    Location
    Scotland
    Age
    60
    Posts
    29
    Rep Power
    0

    Re: Samsung air to water heat pump

    The fault code that comes up is E407 which is compressor off on high pressure. I see no other fault codes. When I run unit I would expect low pressure side to run at 80 psi as its on R410, but low pressure goes down to zero.