    Daikin Ceiling Void FBQ



    The Daikin Ceiling Void unit FBQ has a pump lift of 625mm ..... normally we'd lift and drop into a gravity drain. Has anyone ever tried using 6mm flex pipe and if so what length would be a maximum run, with say a vertical lift of 200mm at the unit, to get it over the joist hieght. I haven't been able to find any reference for pressure drops on 6mm tubing. It's porbably not do able but thought I'd ask.

    Cheers in advance.


    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin Ceiling Void FBQ

    I wouldn't suggest it, the pump might manage to push the water along about 4m of 6mm tubing but to be honest they aren't pressure pumps are they?

    Best bet, discharge into a tank pump and use that to pump through the 6mm tube.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Daikin Ceiling Void FBQ

    I've done it a lot over the years using 3/8 hose. Never been called back and takes dodgy pumps out of the equation.

    Cheers

    Eggs

  4. #4
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Daikin Ceiling Void FBQ

    Also done this a few times, on cassettes, but with 3/8 hose. Where the hose was ran with the pipework same height as top of cassette along a ceiling for about 5-6m to outside.

  5. #5
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Daikin Ceiling Void FBQ

    hi guys,
    Sorry for late response ..... a Holiday got in the way.
    We put a tank pump in eventually, though I have misgivings with any pump where there is a risk of inadequate maintenance. With all the will in the world we can't make customers take up regular maintenance checks. That old devil PPM, you either love it or hate it.