    Daikin Capacity Adaptor - resistor Equivalents - To Remove PJ/AJ Fault Code



    As I could not find a list of adaptor resistances here is a table of what I have found from hunting around online. Enjoy and use at your own peril!

    If you have more info or can help to improve the accuracy it would be much appreciated. The idea is to help people save time and the cost of an adaptor (about 6 pounds) by using a resistor costing about 19p from Maplin and a suitable connector or converting an old adaptor. These are needed to clear a PJ/AJ fault code usually after a pcb has been replaced.
    Attached Files Attached Files
    Last edited by chang1; 16-02-2017 at 07:34 AM.



  2. #2
    Join Date
    Apr 2011
    Location
    England
    Posts
    2
    Rep Power
    0

    Table Text

    TYPE.........ADAPTOR MODEL......PART #.........RESISTANCE
    20............J22..........................066963J.......68 kΩ or 0.068 kΩ
    25............J28..........................066964J.......120 kΩ or 0.120 kΩ
    32............J36/40.....................065331J.......40 kΩ or 0.40 kΩ
    35............J36/40.....................065331J.......40 kΩ or 0.40 kΩ
    40............J45..........................065340J.......0.82 kΩ
    45............J50..........................065334J.......1.5 kΩ
    50 Skyair...J50..........................065334J.......1.5 kΩ
    50............J56..........................064060J.......2.0 kΩ
    60 Skyair...J71..........................065336J.......3.9 kΩ
    63............J71..........................065336J.......3.9 kΩ
    71............J80..........................065341J.......4.7 kΩ
    80............J90..........................066965J.......6.2 kΩ
    100..........J112.........................065337J.......9.1 kΩ
    125..........J140.........................065338J.......13 kΩ
    140..........J160.........................065339J.......16 kΩ
    200..........J224.........................066966J.......33 kΩ or 27 kΩ
    250..........J280.........................067046J.......47 kΩ or 33 kΩ

    Resistance values from various sources. I think you should use the 2nd value for the ones with 2 values but may be wrong. Type = Capacity Class. Adaptor model number is cooling capacity in kW multiplied by 10. eg. an 8 kW system would use a J80 adaptor. If 2 evaporators are fitted then each would have a J36/40 adaptor fitted.