    Need Help For Short Cycling Of Compressor - 500W Liquid Dispenser



    Dear All,
    I Have Been Working on a 500 W Liquid Dispenser. Compressor is Emerson Based Reciprocating One KCN415LAG.

    Evaporator is a Plate Type Heat Exchanger. During Idle Conditions (i.e.) No Dispense Conditions, It Was Recorded that Thermal On Off Cycles Were Repeating At around 20 Minutes.

    However, Under Dispense Conditions there are Chances that On Off Cycle May Happen during 1 Min Intervals. Nominal Ampere Ratings Taken Were Around 1.6 A to 2A, During Starts Inrush Current Was Observed to be 12A. LRA Rating On Compressor is 14 A. I understand Short Cycling May Affect Life of Compressor. But Can We Overcome This Limitation by Means of Any Accessories Such as Inverter or AC Drives For Limiting Staring Currents? Need Expert Advice on the Same. Thanks.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Need Help For Short Cycling Of Compressor - 500W Liquid Dispenser

    Check any pump down controls or pressure switches, it appears that there may be pressure leaking through shut off valves.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Need Help For Short Cycling Of Compressor - 500W Liquid Dispenser

    Which type of expansion device is on the unit .ie capillary tube or thermostatic expansion valve ?

  4. #4
    Join Date
    Dec 2016
    Location
    India
    Age
    29
    Posts
    4
    Rep Power
    0

    Re: Need Help For Short Cycling Of Compressor - 500W Liquid Dispenser

    Quote Originally Posted by Glenn Moore View Post
    Which type of expansion device is on the unit .ie capillary tube or thermostatic expansion valve ?
    Dear Sir,
    We are Using Capillary Tube 0.050'. Whats Seems To be In Our Application, That there Are Chances that Short Cycling may Happen, However Not Always. In That Case, If To Avoid Any Potential Risks Due to Short Cycling , Can We Add Anything To System.

  5. #5
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,044
    Rep Power
    35

    Re: Need Help For Short Cycling Of Compressor - 500W Liquid Dispenser

    You could try fitting a delay timer, 3 or 5 mins probably be enough.

  6. #6
    Join Date
    Dec 2016
    Location
    India
    Age
    29
    Posts
    4
    Rep Power
    0

    Re: Need Help For Short Cycling Of Compressor - 500W Liquid Dispenser

    Quote Originally Posted by Tayters View Post
    You could try fitting a delay timer, 3 or 5 mins probably be enough.
    Thank You Sir..We Will Consider It.