    Dec 2016
    India
    4
    Need Help For Short Cycling Of Compressor - 500W Liquid Dispenser
    Dear All,
    I Have Been Working on a 500 W Liquid Dispenser. Compressor is Emerson Based Reciprocating One KCN415LAG.
    Evaporator is a Plate Type Heat Exchanger. During Idle Conditions (i.e.) No Dispense Conditions, It Was Recorded that Thermal On Off Cycles Were Repeating At around 20 Minutes.
    However, Under Dispense Conditions there are Chances that On Off Cycle May Happen during 1 Min Intervals. Nominal Ampere Ratings Taken Were Around 1.6 A to 2A, During Starts Inrush Current Was Observed to be 12A. LRA Rating On Compressor is 14 A. I understand Short Cycling May Affect Life of Compressor. But Can We Overcome This Limitation by Means of Any Accessories Such as Inverter or AC Drives For Limiting Staring Currents? Need Expert Advice on the Same. Thanks.
    70
    10,627
    52
    Re: Need Help For Short Cycling Of Compressor - 500W Liquid Dispenser
    Check any pump down controls or pressure switches, it appears that there may be pressure leaking through shut off valves.
    Aug 2014
    434
    Which type of expansion device is on the unit .ie capillary tube or thermostatic expansion valve ?
    Dec 2016
    India
    4
    Quote Originally Posted by Glenn Moore View Post
    Dear Sir,
    We are Using Capillary Tube 0.050'. Whats Seems To be In Our Application, That there Are Chances that Short Cycling may Happen, However Not Always. In That Case, If To Avoid Any Potential Risks Due to Short Cycling , Can We Add Anything To System.
    Apr 2008
    Southampton, England
    43
    922
    29
    You could try fitting a delay timer, 3 or 5 mins probably be enough.
    Dec 2016
    India
    4
    Quote Originally Posted by Tayters View Post
    Thank You Sir..We Will Consider It.