    Chiller Fault



    Couldn't decide whether to post this thread here or in troubleshooting section ?

    York chiller, dreaded fault code-the usual LOW CURR/MP/HP. Chiller doesn't start on the problem circuit, just a couple of clicks and out on the fault, maybe after about 5 seconds. I thought it must have been the mecahnical HP switch when I got there, so had a look, but it had't tripped (pressed the reset but it was already in). Now usually I would have thought that a motor protection fault would not still be there as the compressor (a screw one) was not hot. If there had been another problem I had expected the chiller to start up for at least a few seconds before any current faults could have been detected, so as no current was ever drawn as the contactor never pulled in, I think perhaps the HP switch must have an open fault.

    HELP please.
    Thanks
    James

    PS I was only asked to look on way home so due to time being a bit short was only there 30 minutes and then we had a thunderstorm.


    a problem shared is a problem halved

  2. #2
    Join Date
    Mar 2006
    Location
    England
    Posts
    15
    Rep Power
    0

    Re: Chiller Fault

    Hi James,

    Been a long time since I saw a York chiller now, but one thing worth checking is whether or not both red leds in the top right of the board are lit, which is the big one in the centre compartment behind the display (or it is on the older machines) . This will tell you whether the mp modules are ok. Also in there may be 2 quick blow fuses which are worth checking. The hp switch should be easy to check, failing that you may need to get a drawing.

    Hope this helps a bit

  3. #3
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Chiller Fault

    This is one of the millenium chillers with the microprocessor board. It doesn't have the LED's but I reckon, having reflected on it, that I can sort it out on Tuesday. If the HP has continuity, then it's the mp module, or a phase problem.

    Cheers
    James
    a problem shared is a problem halved

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. carrier chiller fault codes
    By al in forum Air Conditioning
    Replies: 7
    Last Post: 20-07-2009, 10:10 PM
  4. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  5. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •