    Properly designed and operated evaporative condensers don't have subcooling.
    To save energy you should control wet bulb approach(temperature difference between condensing temperature and wet bulb temperature). This approach shows the balance between compressors and condensers capacities. At optimum approach, these capacities are balanced and total (compressors + condensers) energy use is minimal.
    Last edited by Segei; 20-11-2016 at 10:46 PM.