Results 1 to 12 of 12
    63
    4,567
    Standard solenoid coils.
    I may have got it wrong!
    But are the modern Solenoid coils Double insulated!
    Only Most I use, come with an Earth Pin / Terminal.
    Does the Earth terminal perform any purpose?
    Is it actually necessary?
    Thanks Grizzly
    Sep 2003
    ISRAEL
    66
    4,132
    38
    Re: Standard solenoid coils.
    What make are you talking about?
    On Danfoss with the "click" connection, its touching the stem of the valve.
    Other manufacturers have steel sleeve around the stem which is grounded.
    63
    4,567
    So It's relevant then?
    Sep 2003
    ISRAEL
    66
    4,132
    38
    Earth is always important, it's to save your life!!
    There are two common faults with solenoid coils, short winding > will trip control switch. Short circuit between ground and neutral > will trip pcb.
    Grounded systems is very important,
    Jun 2011
    Australia
    38
    306
    Photo shows electrical connection between solenoid earth pin & valve body..IMG_1815.jpg
    Mankind does not know why Coffee make us poop..
    https://m.youtube.com/watch?v=U8Fqyyv16SM
    68
    3,362
    Hi Grizzly.
    had a situation recently with a Sporlan industrial S/V with two wire coil connection and metal casing earthed.
    For what ever reason the coil failed , control system C/B tripped and system stopped > Unfortunately the coil failure blew a hole in the solenoid lifting stem. Things got interesting after that, as solenoid was Hp liquid make up valve on ammonia plant. I get called out 6.00am and arrive to WW3, full monty turn out from chemical response team all alarm system worked though and factory cleared. Liquid ammonia pooled on the floor of plant room, stuffed my work boots.
    2,536
    28
    Quote Originally Posted by HVACRsaurus View Post
    i
    The old GPLX solenoid to valve body earth trick!
    63
    4,567
    Thanks Guys.
    I have never knowingly not connected the earth on any Solenoid Valve.
    I just wondered if leaving it off was an option?
    My reason was because recently I was involved in replacing the Oil Capacity Solenoid Block on a 4 year old SAB 193. )Sabroe Screw)
    Which has now uses a re-designed Block.
    With DC coils which has + and - terminals on a pcb within the Din plug. But the earth terminal is below this board on the Terminal Block.
    My colleague and I initially questioned whether we could miss out the Earth connection.
    However the Earth connections were made despite it being a real pig to do.
    But it got me wondering?
    Hence the original question.
    Thanks Guys!
    Ps Magoo I know what you mean about Ruining your boots, been there.
    We are issued with Wellington Boots in our "safety Kit!"
    70
    10,548
    52
    I did read somewhere that if you use the earth terminal in the connector then you shouldn't also put an earth wire onto the earth screw of the valve body if one is fitted.
    Sonething to do with potential differences but over my head.....
    Oct 2008
    newbury
    56
    1,370
    29
    Quote Originally Posted by chemi-cool View Post
    Come live in Tenerife.. E is optional and usually not present :-)
    Nov 2009
    france
    58
    135
    12
    Hi to all,
    coil must be grounded, it's in the Parker instructions.
    I have a test report from Parker for those who would like some more explanations
    Aug 2004
    746
    When I was last in Tenerife E's were obligatory. ...old ravers never die.
