    Standard solenoid coils.



    I may have got it wrong!
    But are the modern Solenoid coils Double insulated!
    Only Most I use, come with an Earth Pin / Terminal.
    Does the Earth terminal perform any purpose?
    Is it actually necessary?
    Thanks Grizzly


    Despite the High Cost of Living it still remains Popular!

  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Standard solenoid coils.

    What make are you talking about?

    On Danfoss with the "click" connection, its touching the stem of the valve.
    Other manufacturers have steel sleeve around the stem which is grounded.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Standard solenoid coils.

    So It's relevant then?
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Standard solenoid coils.

    Earth is always important, it's to save your life!!

    There are two common faults with solenoid coils, short winding > will trip control switch. Short circuit between ground and neutral > will trip pcb.

    Grounded systems is very important,

  5. #5
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    337
    Rep Power
    21

    Re: Standard solenoid coils.

    Photo shows electrical connection between solenoid earth pin & valve body..IMG_1815.jpg

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Standard solenoid coils.

    Hi Grizzly.
    had a situation recently with a Sporlan industrial S/V with two wire coil connection and metal casing earthed.
    For what ever reason the coil failed , control system C/B tripped and system stopped > Unfortunately the coil failure blew a hole in the solenoid lifting stem. Things got interesting after that, as solenoid was Hp liquid make up valve on ammonia plant. I get called out 6.00am and arrive to WW3, full monty turn out from chemical response team all alarm system worked though and factory cleared. Liquid ammonia pooled on the floor of plant room, stuffed my work boots.

  7. #7
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Standard solenoid coils.

    Quote Originally Posted by HVACRsaurus View Post
    Photo shows electrical connection between solenoid earth pin & valve body..IMG_1815.jpg
    i

    The old GPLX solenoid to valve body earth trick!

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Standard solenoid coils.

    Thanks Guys.
    I have never knowingly not connected the earth on any Solenoid Valve.
    I just wondered if leaving it off was an option?
    My reason was because recently I was involved in replacing the Oil Capacity Solenoid Block on a 4 year old SAB 193. )Sabroe Screw)

    Which has now uses a re-designed Block.
    With DC coils which has + and - terminals on a pcb within the Din plug. But the earth terminal is below this board on the Terminal Block.
    My colleague and I initially questioned whether we could miss out the Earth connection.
    However the Earth connections were made despite it being a real pig to do.
    But it got me wondering?

    Hence the original question.
    Thanks Guys!

    Ps Magoo I know what you mean about Ruining your boots, been there.
    We are issued with Wellington Boots in our "safety Kit!"
    Despite the High Cost of Living it still remains Popular!

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Standard solenoid coils.

    I did read somewhere that if you use the earth terminal in the connector then you shouldn't also put an earth wire onto the earth screw of the valve body if one is fitted.

    Sonething to do with potential differences but over my head.....
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: Standard solenoid coils.

    Quote Originally Posted by chemi-cool View Post
    Earth is always important, it's to save your life!!

    There are two common faults with solenoid coils, short winding > will trip control switch. Short circuit between ground and neutral > will trip pcb.

    Grounded systems is very important,
    Come live in Tenerife.. E is optional and usually not present :-)

  11. #11
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    226
    Rep Power
    19

    Re: Standard solenoid coils.

    Hi to all,

    coil must be grounded, it's in the Parker instructions.

    I have a test report from Parker for those who would like some more explanations

    Capture 1.jpg
    Attached Images Attached Images

  12. #12
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    745
    Rep Power
    25

    Re: Standard solenoid coils.

    Quote Originally Posted by r.bartlett View Post
    Come live in Tenerife.. E is optional and usually not present :-)
    When I was last in Tenerife E's were obligatory. ...old ravers never die.