    H.P. Receiver Maintenance



    I need to replace a old isolation v/v on our H.P. Receiver. The v/v is used to isolate the suction accumulator from the receiver. The question is.....is it better to pump out the plant and bring all the liquid back to the receiver which will fill the receiver to about 7/8 full then pump it down to atmospheric pressure to replace the v/v or pump all the liquid out of the receiver then blow it down?



  2. #2
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: H.P. Receiver Maintenance

    It is better to collect liquid somewhere else: evaporators, low pressure receivers, condensers....

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: H.P. Receiver Maintenance

    Do a system pump down and recover refrigerant to service bottles, then repair/ replace service vav on HP receiver.