    Industrial air drier.



    In an air separation plant I have a large air drier with two compressors, one is bigger than the other.

    The unit is controlled by Carel Pco5 and superheat controller. Each compressor has its own speed controller.

    When the first compressor kicks in, it accelerates up to maximum speed and then the second compressor kicks in. At that point the pressure starts to decrease and the units trips on low pressure.

    I am wondering about the sequence of operation regarding the speed of the compressors, should the first one slows when the second one kicks in and maintain the pressure or keep the first one at top speed?

    The sequence of starting changes by 3 min resting time.
    Refrigerant is 410A.
    HGBP is present but I think it might be faulty.[Sporlan HGBE-8]

    Any thoughts? Different ideas?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Industrial air drier.

    After the first has reached full speed I would expect the second one to start at low speed and then ramp up as required to take the load.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Industrial air drier.

    Hi Chemi.
    Most control systems I work on have the scenario where the lead comp ramps up to 100% or Above 80% on others.
    Once the 2nd comp is called for the 1st drops off load and they both load together.
    Normally there is also some form of Suction Ramp / Pressure limiting to stop the LP situation you describe.

    So your asking the right questions and you are correct the load drops off the lead as the lag is started and they then load up slowly.
    I assume there will be relevant settings within the Carel controller to help achieve this?
    (Proportional / Integral control settings ect?)

    Let us know how you get on?
    I am sure there will be others more knowledgeable of the Carel PCo controller that can help.

    Good Luck Grizzly
    Despite the High Cost of Living it still remains Popular!

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Industrial air drier.

    If HGBP is faulty, you will get low pressure trip at start up, also look at LP delay time, may need to adjust upwards by 30 seconds. Bigger compressor starting and ramping up to 100% would make sense, unless load has dramatically fallen off since purchasing the machine i would leave as is. I would possibly look at keeping a compressor running full time, even if air is dry the HGBP would allow machine to keep ticking over until load comes on, the Atlas copco ones do this, biggest problem here is keeping head pressure up, not an issue with you i'd say!
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Industrial air drier.

    Hi Chemi.
    with no HGBP you cannot control the dew point condition and water separation, so system bombs out on low LP. definitely a controller issue or S/v problem.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Industrial air drier.

    Thanks everyone, I will try to get more info on the HGBP today.
    Might have to replace it.
    Will keep you informed of how we get on.