    Fujitsu Cassette problem



    Hi Guys,

    I have a Fujitsu cassette A/C with an issue.
    Model: Indoor AUT30RLD-W Outdoor AOT30RMBL
    When the unit is turned on it runs fine for 10-20 mins cooling good.
    Indoor fan runs fine, the compressor and fan in the condenser come on and run as well.
    The filter is clean etc.
    After the 10-20 mins of fine operation the LCD wall control faults out with EE:EE.

    My question is: How to retrieve the fault code from this model, and the relevant fault codes.

    Many Thanks,
    Keza



  2. #2
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Fujitsu Cassette problem

    To Interrogate
    When E:EE is displayed switch unit off and press the temp up and temp down
    buttons simultaneously for 3 seconds.

    OO ID to RC Comms Fail
    O1 ID to OD Comms Fail
    O2 ID Air Sensor Open
    O3 ID Air Sensor Close
    O4 ID Pipe Sensor Open
    O5 ID Pipe Sensor Close
    O6 OD Pipe Sensor Fail
    O8 Power Source Connection Failure
    O9 Drain Problem Float switch operated
    OA OD Air Sensor Fail
    OC Discharge sensor Fail
    OE Outdoor High Pressure Heatsink error
    11 OD PCB Fail
    12 ID Fan Fail
    13 OD Signal Abnormal ID signal error
    14 OD EEPROM Fail
    15 Compressor Temp Failure
    16 Pressure Switch Error
    17 IPM Error
    18 CT Error
    19 Active Filter Module Error
    1A Compressor Failure
    1B OD Fan Failure
    1C Inverter to PCB Comms Fail
    1D 2 Way Valve sensor Fail
    1E Expansion Valve Error
    1F Connection ID Unit Error
    20 Indoor manual switch abnormal
    24 Excessive high pressure protection on cooling

    25 PFC circuit error
    26 Indoor signal error
    27 Indoor signal error
    28 Indoor heat exchanger temperature error
    29 Outdoor heat exchanger temperature (middle) error
    2A Power supply frequency detection error
    2B Compressor temperature error
    2C Four-way valve abnormal

  3. #3
    Join Date
    Aug 2014
    Location
    Australia
    Age
    36
    Posts
    68
    Rep Power
    10

    Re: Fujitsu Cassette problem

    Thanks mate will try that on site tomorrow

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Fujitsu Cassette problem

    Don't switch the power off or you will lose the error code...just switch the unit to Off on the controller

  5. #5
    Join Date
    Aug 2014
    Location
    South Africa
    Age
    41
    Posts
    26
    Rep Power
    0

    Re: Fujitsu Cassette problem

    could be a condensate pump problem.

  6. #6
    Join Date
    Aug 2014
    Location
    Australia
    Age
    36
    Posts
    68
    Rep Power
    10

    Re: Fujitsu Cassette problem

    Hi guys,
    Thanks for all answers

    Just an update.
    Got the error code- E:00- Communication error between indoor unit and controller.
    I called Fujitsu tech support got thier test sheet emailed to me.
    Checked for 12v dc between 1 and 3 terminal on wall controller= yes
    Checked for fluctuating 7v-12vdc between terminal 3 and terminal 2 on the wall controller with the cable from the indoor unit disconnected from terminal 2= yes
    Checked for fluctuating 7v-12vdc between terminal 3 and the disconnected wire from the indoor unit from terminal 2= No
    This brings my attention to the indoor unit.
    Checked condensate pump, tested for a circuit through its plug as advised by fujitsu.
    Checked fan motor windings
    Checked thermistors to have no open circuits.
    Checked fan capacitor
    My final conclusion is that it's an intermittent fault with the indoor control board.
    The unit runs fine for 10-20 mins then faults out.
    The cable to the controller is also shielded and earthed at the indoor unit.

    Such a tricky fault.

    Let me know your thoughts guys.

    Cheers,
    Kez

  7. #7
    Join Date
    Aug 2014
    Location
    Australia
    Age
    36
    Posts
    68
    Rep Power
    10

    Re: Fujitsu Cassette problem

    Update:
    Got the go-ahead from the client to replace the indoor control board. Unit now working like a dream.