Results 1 to 12 of 12
    Somerset
    64
    4,587
    Sight Glass above and parallel to liquid line?
    I was looking at a Italian Chiller on Friday, which had a liquid line sight glass.
    The sight Glass is suspended above the Liquid Line.
    Which has short 1/4" pipe tails either side of it tapped into the Liquid Line.
    Does anyone no why this setup is preferred by some?
    Surely being above the Liquid Line can cause a false indication of flow?
    Jul 2006
    68
    735
    Re: Sight Glass above and parallel to liquid line?
    I have seen this done. It was installed in order to use the moisture indicator in the small glass.
    Sep 2003
    ISRAEL
    66
    4,153
    38
    I do it all the time, it saves space, money and time.
    Use it from 3\4 and up.
    Jul 2006
    68
    735
    Grizzly:
    I bow to your knowledge.
    Somerset
    64
    4,587
    Grizzly:
    You Got me my friend!
    I am asking because it got me wondering what was the benefit of this design?
    I assume the sight glass would be starved first.
    Just hoping someone knows more than me.
    Feb 2007
    2,477
    Dear Mr Bear,
    Especially on liquid lines with larger diameters it used to be the norm many moons ago when I still did "proper" refrigeration. It kept the costs down at installation but still gave a fairly good indication of charge and flow, not to mention that the moisture indicator still worked.
    Also worth remembering is that when the refrigerant flows through the liquid line any gas bubbles will be suspended in the liquid and not separated at the top of the pipe with liquid flowing at the bottom, this means that a (flowing) sample of the liquid/gas mixture will be fairly representative of what is flowing through the pipe as a whole.
    Jul 2006
    68
    735
    Guess I should have replied to Chemi-cool.
    Just age I guess!
    44
    3,800
    38
    Remember seeing a diagram of how to pipe one in, the smaller pipe should enter the bigger one at 45' and have its end cut off at 45' so as to be parallel to the flow in the main pipe and terminate at the center of the bigger pipe. Only benefit i can see is cheapness unless the liquid line is above the size sight glasses are available for.
    Somerset
    64
    4,587
    Thanks Guys!
    A rep point for Viking's concise answer.
    Thank you.
    And thanks to NH3LVR.
    For allowing me to realise that its not just me that gets it wrong sometimes!
    Cheers Guys!
    Somerset
    64
    4,587
    Thanks Guys!
    Thank you.
    Cheers Guys!
    Interesting info MS.
    I was wondering how the flow was directed through the sight glass.
    What you say makes sense.
    Thanks.
    2,579
    29
    Grizzly, Example from Sporlan
    http://sporlanonline.com/literature/70/70-10.pdf
    Somerset
    64
    4,587
    Hi Ranger
    Sadly I cannot yet give you a rep point.
    Your link is very interesting as Sporlan show the sight glass in the vertical or on the side of the horizontal liquid line.
    Which makes sense to me, however the one which I was looking at on Friday is mounted on the top of the liquid line.
    They also state on lines above 2,1/8"!
    Not sure what actual size these are.
    I wasn't looking at the size. Just the configuration.
    Excuse my poor photography the photo is shown on its side.
    The liquid line is actually horizontal (Clockwise 90 degrees!)