    Roof Top vs Ceiling units



    Hi all,
    Your Suggestions and comments would be appreciated;
    A hall of 680 sq. m floor area, with a seated capacity of 900, which at times is also being used to host special Fairs with multi stalls.
    1. Would it be appropriate for a ground level air flow or overhead air flow?
    2. Would roof top package unit or stand alone ceiling split units be ideal?
    3. What would be the ideal cooling capacity required- Bearing in mind that we are in a tropical climate with the mercury nearing 46 deg. centigrade.

    Tks & Regards

    Pravin



  2. #2
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Smile Re: Roof Top vs Ceiling units

    hi sir

    the a/c system is preferably to throw the cool air on the faces of resedance, so a floor unit is beter, and install it about 1.5 meter over the ground(this is the breathing line)
    another benefit of floor unite is:easy mentenance

    also to be on safe side, install multy separate a/c systems, if any one is faulty for any reason,you can depend upon the others
    about the capacity you need, thes is depend on the wall thickness,type of brick,temp.deferance,windows,,,,,etc.
    but i have conservative measurment for a/c capacity is that:
    8 square meters of aria needs 1 ton of refrigeration
    good luck

  3. #3
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Roof Top vs Ceiling units

    only for your reference
    1. it's better to use ground level air flow by the air supply outlet beside the seat and the exhaust push out from above
    2.roof top unit is better for it's easy to arrange the air flow
    3. need calculate carefully,if by raw estimate,it should be up to 300w/m2(not exactly,just by me. suggest apply ERV for saving energy.

    regards
    LC
    I hear...I forget;I see...I remember;I do...I understand

  4. #4
    Join Date
    Feb 2006
    Location
    Mauritius
    Posts
    15
    Rep Power
    0

    Re: Roof Top vs Ceiling units

    Hi Afeef,
    Thank so much for your reply. As a matter of fact there is an existing air cooled liquid chiller of the 30 GF series having 3 compressors Carlyle 06EF 299. Two air handling units discharge in two ducts which are at floor level. The problem arises when stalls are set up in the hall. The stalls leave a clearance of not more than 50 cms from the ducts, which rtesult in hot spots at the centre of the hall and due to frequent problem and abrupt faults of the existing chiller, the whole air conditioning system is to be replaced. The dimensions of the Hall is as follows; L 31.40M x W 21.68m x H 10.0m. What would be the best alternative to the existing carrier chiller?

    Regards

    pravin

    Quote Originally Posted by afeef
    hi sir

    the a/c system is preferably to throw the cool air on the faces of resedance, so a floor unit is beter, and install it about 1.5 meter over the ground(this is the breathing line)
    another benefit of floor unite is:easy mentenance

    also to be on safe side, install multy separate a/c systems, if any one is faulty for any reason,you can depend upon the others
    about the capacity you need, thes is depend on the wall thickness,type of brick,temp.deferance,windows,,,,,etc.
    but i have conservative measurment for a/c capacity is that:
    8 square meters of aria needs 1 ton of refrigeration
    good luck

  5. #5
    Join Date
    Feb 2006
    Location
    Mauritius
    Posts
    15
    Rep Power
    0

    Re: Roof Top vs Ceiling units

    Hi Lc Shi,
    Thank so much for your reply. As a matter of fact there is an existing air cooled liquid chiller of the 30 GF series having 3 compressors Carlyle 06EF 299. Two air handling units discharge in two ducts which are at floor level. The problem arises when stalls are set up in the hall. The stalls leave a clearance of not more than 50 cms from the ducts, which rtesult in hot spots at the centre of the hall and due to frequent problem and abrupt faults of the existing chiller, the whole air conditioning system is to be replaced. The dimensions of the Hall is as follows; L 31.40M x W 21.68m x H 10.0m. What would be the best alternative to the existing carrier chiller?

    Regards

    pravin




    Quote Originally Posted by Lc_shi
    only for your reference
    1. it's better to use ground level air flow by the air supply outlet beside the seat and the exhaust push out from above
    2.roof top unit is better for it's easy to arrange the air flow
    3. need calculate carefully,if by raw estimate,it should be up to 300w/m2(not exactly,just by me. suggest apply ERV for saving energy.

    regards
    LC

  6. #6
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Roof Top vs Ceiling units

    Hi Sir
    i'm not sure if change all the system including the air duct or only change the chiller. Do you confirm the capacity is OK? how about the fresh air supply? suggest buy module chiller easy to adjust capacity to meet load change and abrupt failure.


    rgds
    LC
    I hear...I forget;I see...I remember;I do...I understand

Similar Threads

  1. What units you'll see in your country?
    By nova in forum Transport
    Replies: 25
    Last Post: 07-11-2010, 02:31 PM
  2. ceiling concealed multi split
    By SIRROM in forum Air Conditioning
    Replies: 7
    Last Post: 22-08-2006, 01:47 PM
  3. Mitsibishi VRV System 8 out of 10 units work
    By moondawn in forum Air Conditioning
    Replies: 5
    Last Post: 29-09-2005, 11:02 PM
  4. Highcool split air con units
    By iceman007 in forum Air Conditioning
    Replies: 10
    Last Post: 31-05-2005, 12:31 PM
  5. AC units as cooling units
    By Peter_1 in forum Commercial
    Replies: 11
    Last Post: 18-03-2005, 06:42 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •