    Dfa75b1 daikin inverter fan testing



    I'm really stocked I'm not very used to inverter motors. Please is it possible to start the inverter fan using direct AC or DC VOLTAGE ? I want to ascertain the condition of the fan motor. please.



  2. #2
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: Dfa75b1 daikin inverter fan testing

    look the manufacture's data..do not make experiments with electricity!

  3. #3
    Join Date
    Oct 2016
    Location
    Nigeria
    Age
    42
    Posts
    6
    Rep Power
    0

    Re: Dfa75b1 daikin inverter fan testing

    Thank you please can you help with a link to the Inverter fan manufacturers data? It has no electrical parameters

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Dfa75b1 daikin inverter fan testing

    Can't find your model reference but assuming that the motors are similar download the 'M' series manual from here....

    http://www.daikinac.com/content/reso...anuals/skyair/

    Goto page 170 to read the motor checks.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2016
    Location
    Nigeria
    Age
    42
    Posts
    6
    Rep Power
    0

    Re: Dfa75b1 daikin inverter fan testing

    thank you Brian I got the fan check steps. I will try it and publish my result.

  6. #6
    Join Date
    Oct 2016
    Location
    Nigeria
    Age
    42
    Posts
    6
    Rep Power
    0

    Re: Dfa75b1 daikin inverter fan testing

    I did the fan voltage test and I got 4.8v and 15.9v between pin 1 and 4, and pin 3 and 4 respectively which seem that the fan is ok. there 2 outdoor units synchronised. one of the fan in the second unit is bad. please how can I switch mode for one of the units to start? VRV IV INVERTER TYPE OUTDOOR UNIT.

  7. #7
    Join Date
    May 2010
    Location
    Seoul
    Posts
    2
    Rep Power
    0

    Re: Dfa75b1 daikin inverter fan testing

    Do not supply AC power to DC motor, it will damage the coil.
    There is some tool to check the inverter board's fault or motor's fault itself.

    http://www.ebay.com/itm/Inverter-Pha...HwAAOSw0fhXj1y-

  8. #8
    Join Date
    Oct 2016
    Location
    Nigeria
    Age
    42
    Posts
    6
    Rep Power
    0

    Re: Dfa75b1 daikin inverter fan testing

    thank you Mistyjune. I confirmed the fault is from the fan motor. pls how can I deactivate one of the outdoor units and run one of the units while expecting a new fan.

    2. please I need link to inverte fan supplier model DFA75B1 for VRV unit.

  9. #9
    Join Date
    Oct 2016
    Location
    Nigeria
    Age
    42
    Posts
    6
    Rep Power
    0

    Re: Dfa75b1 daikin inverter fan testing

    please what is the proper direction of air in the outdoor evaporator? is it upward away from the unit or downward into the unit. because my unit is still showing error code E7-18 while the outdoor fan turns anticlockwise (dragging air downward into the unit).

    please what is the possible solution