    Power Factor for Copeland ZP series 3 Phase Scroll Compressor



    I'm interested in estimating input power on a 208/3/60 ZP scroll compressor. I have a CT installed over one leg and assuming that the motor coils are balanced and that phase to phase voltage is 208V all I need to know to estimate the power consumption is the power factor for this compressor.

    Power in kW = Amps x 3 x 208 / 1.73 * PF / 1000

    When I use a PF of 0.9 I seem to be getting higher input power than expected under the load conditions. So either 0.9 is too high or I need to use a corrective factor for the inexpensive 0-5V CT being used.

    Anyone know where to obtain the PF for such a compressor or whether it is to be expected that a corrective factor be used with an ordinary CT in a 3P environment?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Power Factor for Copeland ZP series 3 Phase Scroll Compressor

    How do your results compare with the manufacturers published input figures?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Power Factor for Copeland ZP series 3 Phase Scroll Compressor

    a good power factor is around 0.98 to 0.99 which indicates efficient use of drawn power consumed, another factor not in your formula is motor efficiency. should be around 0.9 hopefully.
    so as total efficiency increases the drawn power current should reduce.
    Power factor capacitors basically balance drawn current to even things out so to speak, dropping the total average.
    On large plants automatic power factor correction can reduce power costs hugely, controlling inductive and resistive loads, and peak load penalties.

  4. #4
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    181
    Rep Power
    14

    Re: Power Factor for Copeland ZP series 3 Phase Scroll Compressor

    is there any good stack of information with regard to power factor and total efficiency?

  5. #5
    Join Date
    Aug 2013
    Location
    Canada
    Age
    58
    Posts
    4
    Rep Power
    0

    Re: Power Factor for Copeland ZP series 3 Phase Scroll Compressor

    Quote Originally Posted by Brian_UK View Post
    How do your results compare with the manufacturers published input figures?
    That's the problem - input power is higher than max draw values published. The output is bang on and COP is influenced by both of course.

    I'm thinking the problem lies with the off-the-shelf CT's which may need a corrective factor to be used in 3 phase applications. However, even with such a correction I would still like to know where to find the power factor.

    With regards to the other reply which mentioned capacitors - there are none used in this light commercial 10 ton unit.