    Electronic flow switch carrier 30XA Chiller
    Good day everyone! Can anybody explain how the electronic flow switch with four (4) wires connection in 30XA Chiller works and how it can be troubleshoot to ascertain wether it's defective or still ok? May God bless you all!
  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    63
    Posts
    4,529
    Rep Power
    38
    Re: Electronic flow switch carrier 30XA Chiller
    Hi Okonedo
    With the little info I have, as far as I can make out there should be an input on Terminal 7 of the Master controller.
    I cannot make out whether it is volt free or low voltage?
    But the switch makes or brakes an input into term 7.
    Grizzly
    Despite the High Cost of Living it still remains Popular!
  3. #3
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    26
    Rep Power
    0
    Thank you very much Mr Grizzly. I really appreciate your time and effort. I will check the terminal 7 on the main board.