    Slaughter House meat processing area(slaughter line process)fresh air requirement??



    What is the amount of fresh air required on slaughter line meat processing area( but not ready to eat meat processing) which is fully air conditioned?? What will be the air filtration requirement??
    Meat processing I meant is stages from Cattle dehiding to cutting carcass to quarter before precooling at cold storage from around 30 deg C to 0~1 DegC at. 90% RH



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Slaughter House meat processing area(slaughter line process)fresh air requirement

    Maximum fresh air and full extract and maintain partial pressurization, prechill supply air and ultra filtration. Plus maintain a suitable interior dry bulb condition of average 15' C .

  3. #3
    Join Date
    Dec 2011
    Location
    Navi Mumbai (New Mumbai), India, India
    Age
    36
    Posts
    7
    Rep Power
    0

    Re: Slaughter House meat processing area(slaughter line process)fresh air requirement

    Thank you very much for the reply.
    Do you mean 100% outdoor air/once through required? Does EU-7 Filtration is fine?

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Slaughter House meat processing area(slaughter line process)fresh air requirement

    Yes full fresh plus average 10 % and full extract so a once through air flow, the extra 10% ensures partial pressurization so there is coverage out flow through building structure keeping out flies and crawling insects through gaps. dependent on local space conditions you have to maintain a chilled environment for reducing bacterial accumulation and getting rid of smells etc.. Introduced air should have several levels of air filtration, large lumps as in birds insects etc., pre filters for dust and similar and high efficiency particulate separation / HEPA filters including carbon filters. All dependent on local regulations.
    Slaughter houses are steamy messy and smelly places with blood and offal and excrement, bacteria central. Plus you should select air locks between slaughter area and blast chill areas. same after chill areas and boning out areas, called controlled non cross contamination management.

  5. #5
    Join Date
    Dec 2011
    Location
    Navi Mumbai (New Mumbai), India, India
    Age
    36
    Posts
    7
    Rep Power
    0

    Re: Slaughter House meat processing area(slaughter line process)fresh air requirement

    Quote Originally Posted by Magoo View Post
    Yes full fresh plus average 10 % and full extract so a once through air flow, the extra 10% ensures partial pressurization so there is coverage out flow through building structure keeping out flies and crawling insects through gaps. dependent on local space conditions you have to maintain a chilled environment for reducing bacterial accumulation and getting rid of smells etc.. Introduced air should have several levels of air filtration, large lumps as in birds insects etc., pre filters for dust and similar and high efficiency particulate separation / HEPA filters including carbon filters. All dependent on local regulations.
    Slaughter houses are steamy messy and smelly places with blood and offal and excrement, bacteria central. Plus you should select air locks between slaughter area and blast chill areas. same after chill areas and boning out areas, called controlled non cross contamination management.
    Many Thanks for the reply.

    I'm from India and here we don't have codes for slaughter house air conditioning. Could you please provide some reference for international Codes & Regulations for the same.

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Slaughter House meat processing area(slaughter line process)fresh air requirement

    Hi, vineethvknair

    Quote Originally Posted by vineethvknair View Post
    Many Thanks for the reply.

    I'm from India and here we don't have codes for slaughter house air conditioning. Could you please provide some reference for international Codes & Regulations for the same.
    Here you can read something ...

    http://www.fao.org/docrep/003/x6932e/X6932E00.htm#TOC

    http://www.fao.org/docrep/010/ai407e...0.htm#Contents

    http://www.fao.org/docrep/004/t0098e/T0098E00.htm#TOC

    http://www.fao.org/docrep/003/X6552E/X6552E00.htm#TOC

    http://www.fao.org/docrep/004/t0279e/T0279E00.htm#TOC



    hope this will be of some help to you ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •