    Danfoss PM/CVT



    Hello everyone

    I have a Danfoss PM3-20 which controls the oil going to the oil cooler via a CVT servo. Danfoss are forcing us into replacing the PM3 for a ICV/ICS which is ok as it is now quite easy. Now Dean and Wood are saying the CVT for 20-60 degree range are obsolete. Is this so? What are the alternatives?

    Any help appreciated.



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Danfoss PM/CVT

    Piewie,
    There are a few options that can be used.

    Danfoss or similar ORV valve

    http://products.danfoss.com/productr...lating-valves/

    or ICM with ICAD to dial in exactly what you want

    I tried to find something from Hansen, but maybe they don't make equivalent to CVT, as they can interchange pilots.

  3. #3
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    337
    Rep Power
    21

    Re: Danfoss PM/CVT

    +1 Danfoss ORV

  4. #4
    Join Date
    Aug 2010
    Location
    UK
    Posts
    110
    Rep Power
    14

    Re: Danfoss PM/CVT

    Thanks Ranger I suppose if I looked properly at the newer comps on site I would have spotted it. At first I thought this would be too much work! Then I looked and actually it is a better solution. Then I tried getting a price from Danfoss UK agent and that's when I struck out