    Daikin Ducted FCU



    Has anybody had any issues with Daikin FDQ 250 B units? We installed 180 last year, and have recurring issues with Condensate leaks. We've tried everything obvious. Water is getting into the fan section, and leaking out (obviously).



  2. #2
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Daikin Ducted FCU

    Have you installed traps on the drains and are they sized correctly for the static pressure of the FCU's?
    Last edited by Slim R410a; 29-09-2016 at 12:56 PM.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Ducted FCU

    That seems strange as the fan section is behind the coil so should be at a lower pressure than the outlet

    If the condensate is flowing back it must be because there is excessive condensate.

    Possible causes are lack of drainage or cracked drain pan

  4. #4
    Join Date
    Apr 2008
    Location
    australia
    Age
    58
    Posts
    47
    Rep Power
    0

    Re: Daikin Ducted FCU

    Isn't the fan section in front of the coil on the 250, therefore you would need to trap the drain?