    Aug 2005
    iraq
    67
    130
    cooling tower & humidity
    dear all
    i know that cooling towers do not be efficient on humid atmosphere ,,,,but what is the maximum relative humidity we can allow to install cooling tower?
    thanks
    Aug 2005
    5,302
    Re: cooling tower & humidity
    afeef,
    The cooling tower capacity quickly reduces as the entering air wet bulb temperature increases. If the entering air relative humidity is 100% then the wet bulb temperature is the same as the dry bulb temperature, so the capacity would be almost zero.
    You can derate the tower capacity for higher entering air wet bulb temperatures but this has the effect of increasing the tower cost and size.
    When the wet bulb temperature begins to reach 80F (26.6C) the tower sizes, costs, and capacities change very quickly.
    Aug 2005
    5,302
    afeef,
    Here is some additional information that may be helpful to you.
    http://www.marleyct.com/catlinks/CTII-1.pdf (168 kb)
    There are lot of good technical topics on water cooling towers also at:
    http://www.marleyct.com/publications.asp
    Aug 2005
    iraq
    67
    130
    thanks us iceman
    god bless you
    Aug 2005
    5,302
    Glad to help afeef. I hope the information is useful.
  1. Cooling Tower Design
    By jteixiera in forum Tools and Calculators
    Last Post: 31-01-2006, 12:23 AM
  2. cooling tower without fillings
    Last Post: 27-12-2005, 12:55 AM
  3. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Last Post: 14-10-2005, 06:34 PM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Last Post: 13-10-2005, 05:14 AM
  5. Cooling tower water pumps
    By reggie in forum Fundamentals
    Last Post: 13-08-2003, 08:18 PM