Midd-temperature R290 refrigeration system
Hello guys,
I would like to design refrigeration system of 1,5 kW cooling capacity. If take to account new f-gas regulation I decided to design system wich will run on R290. To consider compressor is easy, there is a lot of them designed to operate with propane.
My question, is there any special requirement for heat exchangers if I use propane as refrigerant?
-
28-09-2016, 02:04 PM #2
Re: Midd-temperature R290 refrigeration system
.
NO, evaporators are fine but be careful with the fans.
The fans need to be X rated so they don't spark.
Rob