    Hitachi utopia fan error



    • I have 2 indoor cassettes off one condenser
      units indoor are both - rci6 ofsne

      i have a rav12 outdoor unit.

      The fault has occurred as I changed the indoor fan motor as it was noisy , it was working absolutely fine .

      it came up with 19 error code , this relates to fan motor fault .
      if I reset it spins fast for 30 secs then idols then fast then goes into fault error 19.
      i spiked with Hitachi tech and they advised replacing both power and control board .
      I fitted them today and the same is happening , I also put the old motor back on and it does exactly the same .

      my question is what else could make it operate like this ?
      apart from fan or pcb as these have been changed.

      to clarify its 8 year old , never had issue untill I changed motor .
      capacitys all checked and ok .

      help !!





      Blog this Post






  2. #2
    Join Date
    Mar 2009
    Location
    Uk
    Age
    41
    Posts
    121
    Rep Power
    17

    Re: Hitachi utopia fan error

    The new fan motor may be faulty and damaged both the old and new PCBs. Also this is highly unlikely,
    are you sure the other ceiling cassette is not generating the fault? I'd imagine the fault code should have a reference to which indoor it is .

  3. #3
    Join Date
    Dec 2009
    Location
    uk
    Posts
    13
    Rep Power
    0

    Re: Hitachi utopia fan error

    Quote Originally Posted by Neddy View Post
    The new fan motor may be faulty and damaged both the old and new PCBs. Also this is highly unlikely,
    are you sure the other ceiling cassette is not generating the fault? I'd imagine the fault code should have a reference to which indoor it is .

    Hi
    yes it has a unit address , I've been through all thermistor readings on both units , all ok . The other unit runs fine . The faulty unit has had new PCBs , fan motor and loom to motor , I tried un plugging various components but still same fault .hitachi tech are at a loss with what to try next.
    It has no external pump wired in .
    voltages across the boards are ok .

  4. #4
    Join Date
    Dec 2009
    Location
    uk
    Posts
    13
    Rep Power
    0

    Re: Hitachi utopia fan error

    It was the new fan motor in the end ��

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Hitachi utopia fan error

    Thanks for the update and glad that you have resolved the issue.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015