    Swivel couple NPT M TO F 1/2 " leaking



    Hi my mate braze pipe with castel relief valve set and damage swivel coupler.
    I try too lok in York ( chiller was from york) and climate center, Dean and wood and hrp. No one know what is that lol I see that few time in refrigeration systems and chillers. I try contact to castel but they not answer to me and don't know uk dealer .
    Thanks for any help.
    Attached Images Attached Images



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Swivel couple NPT M TO F 1/2 " leaking

    this swivel coupler is for use with hydraulic systems. the inside angle is usually 37 degrees instead of 45 that use in ac.
    You will need to tighten it real hard to stop the leak.
    who ever put it there, used it to reduce diameter for the relief valve.

  3. #3
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    337
    Rep Power
    21

    Re: Swivel couple NPT M TO F 1/2 " leaking

    Hi Mate,

    Go to a Hydraulic Supplies mob (Pirtek?)

    Here it is known as an "AAM" fitting

    Happy tinkering!