    Copeland Scroll Wiring Problem



    Hi

    I've got a job driving me mad atm.

    Single phase Copeland scroll, compressor starts and runs for a short period and then turns off (internal o/load) C-R open circuit.

    I have checked the wiring against our diagram below on the soft start PCB and It is correct.

    When the compressor was running before it cut off I noted the run current as approx:
    Run connection-2~
    Start connection to cap-11~
    Contactor to common- 8~

    I disconnected the start capacitor once the comp was running and the compressor kept going with no problems.

    The run connection current went up to 10~ and the pot seemed much smoother.

    I'm guessing the soft start PCB isn't switching the start winding out? Any thoughts would be appreciated as it seems to be happening on two identical units!!





    image1.PNG



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Copeland Scroll Wiring Problem

    Why use a soft start on a single phase compressor? It's already got a start circuit and a start capacitor.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Copeland Scroll Wiring Problem

    Start capacitor should be switched off at 0.5 to max 2 seconds after start. It is not capable to work longer than that! What is make and model of soft starer? And, as Chemi pointed out, if you use soft starter on single phase unit, than it can affect starting torque of compressor in such way that is not capable of overcoming internal mechanical resistance and cause stalling!
    Last edited by nike123; 12-09-2016 at 09:08 PM.

  4. #4
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Copeland Scroll Wiring Problem

    Its not a recognizable model of soft start.

    Its domestic heat pump perhaps to stop lights dimming.

    Would I be able to wire it direct on and do without the PCB? Wiring diagram?

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Copeland Scroll Wiring Problem

    Of course you can! You need original starting group of compressor in question! What is compressor make and model?

  6. #6
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Copeland Scroll Wiring Problem

    Its a Copeland ZP23K3E-PFJ-522, run capacitor 60uf start cap 100uf

    Im guessing the reason why im having this problem is because the start winding is still "engaged"

    Thanks

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Copeland Scroll Wiring Problem

    You should use correcct soft starter; http://www.actrol.com.au/global/asse...structions.pdf

  8. #8
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Copeland Scroll Wiring Problem

    I'll take a look. Thanks

    If both the start and run capacitors were still in circuit would I see this sort of thing?

  9. #9
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Copeland Scroll Wiring Problem

    If you can put your amp meter round the start capacitor wire you should see an initial peak then drop to nothing as the capacitor is disconnected by the start relay, if the current doesn't stop either the start relay is faulty (welded contacts or such) or the compressor is not starting properly either due to faulty compressor or supply voltage issues.
    Mostly found in Oxfordshire, UK :)

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Copeland Scroll Wiring Problem

    The compressor has its starting relay and doe's automatically and a soft start will kill it.

  11. #11
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Copeland Scroll Wiring Problem

    I finally found the fault. The start capacitor 100uf and run cap 60uf had been swapped over.

    Swapping them back over solved the issue.

    Glad I found it as it would have eventually burnt the winding out