    Three Evaporators, three different evaporation temeperatures



    Hi Guys,
    I have 3 different evaporators - temperatures are -18°C, -10°C and 0°C Evaporation.

    I will place non return valves and the pressure controllers on the evaporators with lower pressure.

    The question would be: what should be taken as evaporation temperature for sizing the compressor? I could easily calculate what would be the temperature of mixed fluids (together with pressure) and i could take that as evaporation temperature but just wanted to know is that the right way.

    how is this sorted with VRF systems?

    BR


    Be careful about reading health books. You may die of a misprint.

  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Tree Evaporators, tree different evaporation temeperatures

    Hi
    As you know you should set your suction in lowest temp .
    but you can not choose all room load to calculate compressor load if it has not unloading system.
    or your compressor should be able works with VFD from lowest load and cover your total load

    Why ?
    because when two of them those not need to works you suction pressure goes to low .
    I think it is better you choose ;
    total load/2

    you need 2 evaporator pressure ( back pressure ) with to check valve and 3 solenoid valve and all
    of them should be have one timer for defrost with 3 contactor / one for each room
    with thermal control of defrost .

    I would say do one unit for each one if your system not to small .
    Last edited by mbc; 12-09-2016 at 02:43 PM.

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Tree Evaporators, tree different evaporation temeperatures

    Hi, MilosBog

    Quote Originally Posted by MilosBog View Post
    Hi Guys,
    I have 3 different evaporators - temperatures are -18°C, -10°C and 0°C Evaporation.

    I will place non return valves and the pressure controllers on the evaporators with lower pressure.

    The question would be: what should be taken as evaporation temperature for sizing the compressor? I could easily calculate what would be the temperature of mixed fluids (together with pressure) and i could take that as evaporation temperature but just wanted to know is that the right way.

    how is this sorted with VRF systems?

    BR
    Your evaporation temperature/pressure should be around -23°C or even lower (dt=5-7K lower then lowest evaporator temperature, in your case evaporator which works at -18°C) ... back pressure controllers you can put only to systems with higher evaporation temp i.e. pressure otherwise will not work ...

    We do not know anything about your system, but it will be much better to install two stage system (for sure more expensive, but definitely much better...)

    Definitely your task is not simple.

    Also for low temperature evaporator you need additional HE (economizer) to sub-cool liquid refrigerant coming from condenser before entering into low temp. evaporator ....

    VRF system (if you are thinking about Variable Refrigerant Flow) cannot be used here ... your system is not HVAC ... it is refrigeration system and some other rules must be applied.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Nov 2010
    Location
    Germany
    Age
    39
    Posts
    120
    Rep Power
    14

    Re: Three Evaporators, three different evaporation temeperatures

    I have noticed now that I had German spell check whilst writing so I got tree instead of three. In such situations when I want to excuse for being lazy to check the spelling I write even more funnier sentences... Anyways Bok Josip and Salam Mbv and thanks for answering.

    I am am bit reluctant to size compressor for the lowest temperature as that particular load is only 5% of all. But what I will try to do is to calculate evaporation temp when all three evaporator are working same time plus for some other cases and I will check out the compressor for all cases.

    I wasnt thinking about using Variable refrigerant flow for this application, I was more interested in how they made it when some evaporator sate working with higher and some with lower temperatures

    do you guys have more suggestions
    br
    Be careful about reading health books. You may die of a misprint.

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Three Evaporators, three different evaporation temeperatures

    hi

    the minimum evaporator temp. is -18

    the 2-stage compressor limit start from - 25 Evap. temp.

    I do not Know Why he can not use VDF ( variable Frequency Drive ) Could say more

    I think he can use VDF By putting Pressure transmitter 4-20 MA and connect that to Analog port in VDF

    and set VDF for that

    by rising pressure in suction line speed of comp goes up .

    setting should take a little more time

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Three Evaporators, three different evaporation temeperatures

    hi MilosBog.
    calculate refrigerant flow rate for each systems operating at average design conditions. That will tell you the compressor swept volume capability required.

  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Three Evaporators, three different evaporation temeperatures

    Hi, MilosBog

    Pozdrav!

    Quote Originally Posted by MilosBog View Post
    I have noticed now that I had German spell check whilst writing so I got tree instead of three. In such situations when I want to excuse for being lazy to check the spelling I write even more funnier sentences... Anyways Bok Josip and Salam Mbv and thanks for answering.

    I am am bit reluctant to size compressor for the lowest temperature as that particular load is only 5% of all. But what I will try to do is to calculate evaporation temp when all three evaporator are working same time plus for some other cases and I will check out the compressor for all cases.

    I wasnt thinking about using Variable refrigerant flow for this application, I was more interested in how they made it when some evaporator sate working with higher and some with lower temperatures

    do you guys have more suggestions
    br
    All is OK we catch almost all

    After reading your answer ... My suggestion is to make all as per mbc suggestion for each system one unit or at least two systems ... one for low temp. system at -18°C and another one for -10°C/0°C systems with back pressure regulating valve for system at 0°C.

    If you want to use only one compressor for all three systems your evaporating temperature/pressure at compressor suction should be at least equal or lower then
    -18°C and of course you need compressor with capacity control when you have reduced load ... of course for that you can use compressor with VFD (variable frequency drive) but set point remain for the lowest requested temperature.

    Note: Hi, mbc
    .... I thought that VRF (Variable Refrigerant Flow) is related to:

    https://www.google.it/search?q=varia...HWoJD68QsAQIag
    or
    https://en.wikipedia.org/wiki/Variable_refrigerant_flow

    and not to VFD - variable frequency drive ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  8. #8
    Join Date
    Nov 2010
    Location
    Germany
    Age
    39
    Posts
    120
    Rep Power
    14

    Re: Three Evaporators, three different evaporation temeperatures

    Pozdravi Josip,greetings fellow Fridgies!
    i will have Variable flow drive on compressor in any case so no worries about that.

    I did some calculations for this for following scenarios:

    low temperature evaporation runs only: compressor suits the needs
    combined flows ( different evaporation temperatures streams mixing together) compressor is sized for this case
    high temperature evaporation runs only : compressor has to work with 75% of capacity

    i will place back flow preventers and for sure internal heat exchanger to stabilize the temperature on suction a bit.

    Thanks to all of you guys!!!